Longevity of 120V- vs. 240V-wired motor?

  • Thread starter Thread starter GregJ7
  • Start date Start date
  • Tags Tags
    longevity Motor
AI Thread Summary
The discussion centers on the wiring options for a 2hp dual-capacitor motor, which can be configured for either 110V or 220V. Performance, including torque, remains consistent regardless of the voltage used, as long as the motor is designed for both. Longevity is influenced more by mechanical factors, such as bearing wear and insulation aging, rather than the voltage configuration itself. While 240V may draw less current and reduce losses, the choice ultimately depends on available circuits and load conditions. Proper installation, including using a suitable power cord and rated capacitors, is essential for optimal motor performance.
GregJ7
Messages
4
Reaction score
2
TL;DR Summary
Wire motor for 120V or 240V?
The 2hp dual-capacitor motor on my bandsaw can be wired for either 220V (draws up to 10 amps) or 110V (draws up to 20 amps). I need to install a new circuit whichever I decide (30 amp circuit for the 110V configuration). Am I correct in assuming the performance of the motor, such as amount of torque in generates, would be the same whichever way I wire it? Is the theoretical longevity of the motor also the same?
 
Engineering news on Phys.org
Honestly, for a specific motor (i.e. one that's already been designed and built), I don't think it matters. I might choose 240 for lower current in the walls, plugs, etc., but that has nothing to do with the motor. There are subtle differences between series and parallel connected windings, but it's the bearings that will probably kill your motor, not the windings.
 
  • Like
Likes russ_watters and GregJ7
I think the longevity of a motor depends more on (a) mechanical strength and absence of vibrations, (b) effectiveness of aging insulation, and (c) the ability of the windings to resist shifting in their mounts.

As a teen, I worked in an amusement park. The roller coaster had a 4HP motor built around the year 1900. It was about 9 feet high and weighed several tons. It ran at 180 RPM (maybe 360). The only maintenance it ever had was a few drops of oil every year. It would be 120 years old today, and it could probably continue another 120 years.
 
GregJ7 said:
Summary:: Wire motor for 120V or 240V?

The 2hp dual-capacitor motor on my bandsaw can be wired for either 220V (draws up to 10 amps) or 110V (draws up to 20 amps). I need to install a new circuit whichever I decide (30 amp circuit for the 110V configuration). Am I correct in assuming the performance of the motor, such as amount of torque in generates, would be the same whichever way I wire it? Is the theoretical longevity of the motor also the same?
I agree with Dave,

The 240V connection will draw less current which could mean lower losses, however it really depends on what you have available. If the motor is designed for 120 or 240, then either will work. I also agree that the bearings would be the first thing to wear out before windings do.
 
You may be creating a false choice for yourself. Although your saw has a 2 HP motor, it won't necessarily operate at anything like that power level - depends on blade loading. Unless you are going to seriously load the saw, you might consider just using it with an existing outlet. You'll know that approach won't work if the breaker trips too often.

Use a short (or heavy, or both) power cord to minimize voltage drop / motor heating (whatever you do).
 
The caps will die long before the bearings, which will die long before the windings.

Make sure the caps are suitably rated if you go for the higher voltage.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...