AI Thread Summary
To calculate power loss due to air filters in residential ductwork, the formula CFM*dP/6356/eff=hp is used, where CFM is the airflow in cubic feet per minute, dP is the pressure drop in inches of water gauge, and eff is the fan efficiency. Typical pressure drops range from 0.1 to 0.2 inches wg, with airflow volumes between 700 and 2000 CFM. A standard HVAC fan efficiency is around 65%. For example, using 2000 CFM at a 0.2" pressure drop results in approximately 0.097 horsepower loss. Understanding this calculation helps assess energy efficiency in HVAC systems.
gm10
Messages
2
Reaction score
0
Hello,

I need a formula to calculate how much power is wasted on different types of air filters. A typical application is a residential central air ductwork. A typical pressure drop is 0.1-0.2 inch wg. Typical volume passing through filters is 700-2000 cfm. A typical filter size is 2-3 sq. ft.

Your help is much appreciated in advance.

gm

This is not a homework. :smile:
 
Last edited:
Engineering news on Phys.org
Welcome to PF. The equation is:

CFM*dP/6356/eff=hp

That's flow in CFM, dP in inches w.g. and efficiency of the fan. A typical good HVAC fan is about 65% efficient, so for example, 2000 CFM at 0.2" is 2000*.2/6356/.65=0.097hp
 
russ,

Awesome. Thanks a lot.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly

Similar threads

Replies
22
Views
3K
Replies
6
Views
7K
Replies
6
Views
16K
Replies
39
Views
14K
Replies
3
Views
3K
Replies
17
Views
7K
Back
Top