Why is my power washer's GFCI plug tripping and getting hot?

  • Thread starter russ_watters
  • Start date
  • Tags
    Power
In summary, the conversation discusses troubleshooting a power washer that has been tripping the GFCI plug when connected to both outdoor and indoor receptacles. The individual took apart the plug and found evidence of water intrusion, but replacing it with a nearly identical plug did not solve the issue. They discuss the difference between 2-wire and 3-wire GFCIs and the potential dangers of using a 2-wire GFCI. They also mention using an electrical socket tester and the possibility of a faulty part in the power washer. Ultimately, they decide to replace the cord with a 3-wire one and use it with a GFCI receptacle for better protection.
  • #1
russ_watters
Mentor
23,163
10,372
I have a small power washer with a two-wire cord and GFCI plug. My outdoor and garage receptacles are on a "house GFCI" circuit, wired in series to one GFCI receptalce.

Yesterday I tried to use the power washer and the plug GFCI would instantly trip when plugged-in and instantly re-trip when reset. It did this when connected either to the outside GFCI receptacle or to an inside, non-GFCI receptacle. And it also got noticably hot.

I took apart the plug (which it was most decidedly opposed to) and found perhaps a little evidence of past water intrusion, despite having a rubber seal. Fine. So I bought a nearly identical plug at Lowes to replace it. I say "nearly" identical because despite an identical body, the new one was three-wire. Same problem.

Should 2-wire vs 3-wire matter? Or, backing-up; I'm having trouble even wrap my brain around the idea of a 2-wire GFCI: since the purpose is to detect an imbalance hot/return, doesn't the ground represent an addtional failure mode and safety that it should have?

With no alternate return path and the power washer not even turned-on (so it was dry), I can't imagine where power might be leaking to cause a trip. Any ideas?

Deciding I a was well-protected by the house GFCI (reasonable assumption?), I replaced the plug with a non-GFCI plug and everything worked fine. I also have a digital power monitor on my house and noticed no change in power draw when I plugged it in, so I'm reasonably confident there was little or no leakage.

Am I missing a danger here?
 
Engineering news on Phys.org
  • #2
Erhmfh; After googling and reading a few stories about people being electrocuted by faulty pressure washers I'm going to toss mine in the trash. I'd still like to understand better what is going on though...
 
  • #3
russ_watters said:
Should 2-wire vs 3-wire matter? Or, backing-up; I'm having trouble even wrap my brain around the idea of a 2-wire GFCI: since the purpose is to detect an imbalance hot/return,
The GFCI detection circuit for 2-wire just looks for an imbalance in the currents in the Hot and Neutral wires. If there is an imbalance, it is assumed to be leaking to Ground.
russ_watters said:
So I bought a nearly identical plug at Lowes to replace it. I say "nearly" identical because despite an identical body, the new one was three-wire. Same problem.
That's weird. Maybe a problem in the power cord near the receptacle that you replaced? When you replaced the Lowe's GFCI receptacle with the non-GFCI plug, how much of the cord did you cut off?
 
  • #4
Maybe also get one of the electrical socket testers and see if the sensitivity level of the Lowe's receptacle is the same as your in-house GFCI. Maybe the in-house one is less sensitive, and the pressure washer did have a slight path to ground that tripped the more sensitive GFCIs...

https://images-na.ssl-images-amazon.com/images/I/41xgYJ1keXL._SL500_AC_SS350_.jpg
41xgYJ1keXL._SL500_AC_SS350_.jpg
 
  • Like
Likes russ_watters
  • #5
So the GFCI was in fact part of the power washer and was getting hot but when replaced with a non GFCI plug and plugged into a GFCI receptacle everything went along fine? Sounds like a bad part of the power washer. If I were you I would replace the cord with a 3 wire and just plug it in the garage GFCI receptacle. That will offer better protection than what was originally there.
 
  • #6
berkeman said:
That's weird. Maybe a problem in the power cord near the receptacle that you replaced? When you replaced the Lowe's GFCI receptacle with the non-GFCI plug, how much of the cord did you cut off?
Zero. The plugs were literally identical except for the missing wire, including that they had a separate compartment for making screw-connections to the wires (in addition to the not quite tamper proof electronics compartment). I did find that odd, but it meant all I needed to do was loosen the connections, pop the grommet out of the old GFCI and pop it all back into place in the new one. The old grommet fit in the new plug and the wires were already stripped and bent to go back into the same screw connections they were in on the old plug.
 
  • #7
Averagesupernova said:
So the GFCI was in fact part of the power washer and was getting hot but when replaced with a non GFCI plug and plugged into a GFCI receptacle everything went along fine? Sounds like a bad part of the power washer.
Yes, and that's what I was thinking: internal problem in the washer, not quite serious enough to trip the house GFCI (which I am certain works because it has tripped in the past).
If I were you I would replace the cord with a 3 wire and just plug it in the garage GFCI receptacle. That will offer better protection than what was originally there.
Well, I would have to find something in the washer to connect the ground wire to. I suppose I could do that and go back to the GFCI, now with 3 wires and if it still trips, then that would point to a more serious internal fault.

I'm also going to take @berkeman's suggestion and get a receptacle tester.

There is another wrinkle here that has me still leaning toward chucking it (beyond the effort factor): my mother wants to borrow it to clean her deck and her house is 30 years old, and I'm pretty sure the outside circuits are not GFCI protected. So if I were to give it to her, it must have a GFCI plug.
 
  • #8
russ_watters said:
Yes, and that's what I was thinking: internal problem in the washer, not quite serious enough to trip the house GFCI (which I am certain works because it has tripped in the past).

Well, I would have to find something in the washer to connect the ground wire to. I suppose I could do that and go back to the GFCI, now with 3 wires and if it still trips, then that would point to a more serious internal fault.

I'm also going to take @berkeman's suggestion and get a receptacle tester.

There is another wrinkle here that has me still leaning toward chucking it (beyond the effort factor): my mother wants to borrow it to clean her deck and her house is 30 years old, and I'm pretty sure the outside circuits are not GFCI protected. So if I were to give it to her, it must have a GFCI plug.
I certainly won't talk you out of taking care of your mum.
-
I also wondered if there were a place on it to connect the ground. Most GFCI receptacles are 5 mA threshold if I am not mistaken. I doubt the GFCI plug that came with the washer is more sensitive than that. Did the GFCI plug you bought at Lowe's get hot as well?
 
  • #9
BTW, if it's a resistive fault, you can measure that with a DVM on the Ohm setting. If it's a 60Hz capacitive fault, you won't see that with a DVM.
russ_watters said:
Well, I would have to find something in the washer to connect the ground wire to.
So with a 2-wire GFCI plug and the washer sitting on dry ground, it still tripped? That's weird, and sounds like a faulty GFCI circuit. Where could the current go?
 
  • Like
Likes Averagesupernova
  • #10
Averagesupernova said:
Did the GFCI plug you bought at Lowe's get hot as well?
It wasn't plugged in long enough to find out -- I was out of troubleshooting mode by then.
 
  • #11
berkeman said:
So with a 2-wire GFCI plug and the washer sitting on dry ground, it still tripped? That's weird, and sounds like a faulty GFCI circuit. Where could the current go?
Yes, I was scratching my head about that too...

...caveat though; I had a rubber hose plugged into it and at least partially charged. The tap was on, but I keep the hose empty, so it was filled almost entirely with air. Seems a long shot, but I suppose it could have been damp enough inside to carry some return current. A very long shot though, since the power washer has a cumbersome/low quality, plastic, removable quick-connect fitting to connect to the hose. That should have been totally dry, but maybe it doesn't take much.

...if I feel like it I might put the GFCI plug back on and plug it in with the hose disconnected to see if it still trips.
 
  • #12
russ_watters said:
...if I feel like it I might put the GFCI plug back on and plug it in with the hose disconnected to see if it still trips.
Try plugging the GFCI plug into power without reconnecting the wires, just the GFCI itself.

p.s. It's common for them to run a little warm even with no load.
 
  • Like
Likes russ_watters
  • #13
Try plugging the washer into a normal outlet and putting an accurate clamp meter around the hot and neutral together. Any net (leakage) current difference will show up.
 
  • Like
Likes russ_watters
  • #14
Tom.G said:
Try plugging the GFCI plug into power without reconnecting the wires, just the GFCI itself.
Great/clever idea. Indeed, they both function normally, indicating it is definitely a problem with the washer. Next step will be to take it apart.

FYI, here's what the GFCI plugs look like:

GFCI.jpg
 
  • #15
russ_watters said:
Next step will be to take it apart.
Well, those sure came from the same factory.

If you have an Ohmmeter, before disassembly check resistance from the power cord (each conductor individually) to the frame of the thing. Both with the switch ON and OFF. That could help localize the problem. A reading below 25kΩ may well trip a GFCI due to capacitive coupling of the frame to the rest of the Universe. (or thru the water source.)

A prime suspect, in my opinion, is moisture in the motor; perhaps because of a bad shaft seal at the pump. Another possible, a dead insect in it somewhere.

Or, before tearing it apart, you could let it sit in direct Sun for a day or two to dry it out.
 
  • Like
Likes jim hardy and russ_watters

1. What is a GFCI?

A GFCI, or Ground Fault Circuit Interrupter, is a device that protects against electric shock by quickly shutting off power to a circuit when it detects a ground fault or imbalance in the electrical current.

2. Why is a GFCI important for a power washer?

A power washer uses high pressure water and electricity, which can be a dangerous combination. A GFCI helps protect against electric shock by immediately stopping the flow of electricity if it detects a ground fault caused by water or other conductive materials.

3. How do I know if my power washer has a GFCI?

Many modern power washers come with built-in GFCI protection, which is indicated by the presence of a "Test" and "Reset" button on the unit. You can also check the owner's manual or contact the manufacturer to confirm if your power washer has a GFCI.

4. Can I use a GFCI extension cord with my power washer?

Yes, you can use a GFCI extension cord with your power washer for added protection. However, it is important to make sure that the extension cord is rated for outdoor use and has the appropriate amperage for your power washer.

5. How often should I test my power washer's GFCI?

It is recommended to test your power washer's GFCI once a month to ensure it is functioning properly. This can be done by pressing the "Test" button and then the "Reset" button to restore power. If the GFCI does not trip, it may need to be replaced.

Similar threads

  • Electrical Engineering
Replies
33
Views
559
  • Electrical Engineering
2
Replies
38
Views
5K
  • Electrical Engineering
Replies
6
Views
3K
Replies
5
Views
1K
Replies
13
Views
916
  • Electrical Engineering
Replies
6
Views
2K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
33
Views
4K
  • Electrical Engineering
Replies
17
Views
2K
Replies
7
Views
1K
Back
Top