The discussion centers on a steam boiler issue where steam at 40 psi has damaged a copper heat exchanger over two years. The user questions whether steam velocity, influenced by the boiler's 2,000,000 BTU rating and the 1-inch pipe size, contributes to this damage. Responses clarify that the BTU rating does not significantly affect steam velocity and suggest that corrosion, particularly from galvanic action between copper and steel, is likely the cause. The location of the hole in the heat exchanger is crucial for diagnosing the problem, as bends in the piping may exacerbate wear. Overall, the issue appears to be more related to material compatibility and corrosion than to steam velocity.
RHorseUSMC
Messages
3
Reaction score
0
I am trying to figure out a problem we are having with a steam boiler. First, it is a natural gas fueled boiler rated at 2,000,000 BTU. In the summer time, the boiler supplies heat to the indoor pool through a heat exchanger. There is approximately 10 ft of 1 inch black iron pipe feeding into the top of of the copper heat exchanger. The problem is that over a 2-year period the steam coming into the heat exchanger @ 40 psi has cut a hole into the heat exchanger. My question is does velocity have any part in this? Someone had told me that do to the size of the boiler (2,000,000 BTU) and the size of the pipe feeding the heat exchanger, the velocity of the of the steam is higher and therefore creating a hole in the heat exchanger. Is there a formula to figure this or can anyone just explain it to me. Thank you--Rick
 
Engineering news on Phys.org
No, the BTU rating has very little to do with the pressure/velocity of the steam in the system (ie, a vastly oversized boiler would simply fire less often and produce roughly the same pressure/velocity). What you have there is probably due to corrosion.

Where is the hole, exactly? I'm pretty sure that copper and steel are the metals that don't work-and-play-well-with-others in plumbing. Ie, if you put them near each other without a dielectric fitting to separate them, they will create a galvanic cell and quickly dissolve the steel.
 
Last edited:
It could very well be an erosion issue. Usually a heat exchanger won't be made entirely out of copper, just the core. Where exactly is the hole in the heat exchanger? Does it happen at a 90° bend? I am imagining a shell and tube heat exchanger. Is this correct?
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...