Question about steam pressure and velocity

AI Thread Summary
The discussion centers on a steam boiler issue where steam at 40 psi has damaged a copper heat exchanger over two years. The user questions whether steam velocity, influenced by the boiler's 2,000,000 BTU rating and the 1-inch pipe size, contributes to this damage. Responses clarify that the BTU rating does not significantly affect steam velocity and suggest that corrosion, particularly from galvanic action between copper and steel, is likely the cause. The location of the hole in the heat exchanger is crucial for diagnosing the problem, as bends in the piping may exacerbate wear. Overall, the issue appears to be more related to material compatibility and corrosion than to steam velocity.
RHorseUSMC
Messages
3
Reaction score
0
I am trying to figure out a problem we are having with a steam boiler. First, it is a natural gas fueled boiler rated at 2,000,000 BTU. In the summer time, the boiler supplies heat to the indoor pool through a heat exchanger. There is approximately 10 ft of 1 inch black iron pipe feeding into the top of of the copper heat exchanger. The problem is that over a 2-year period the steam coming into the heat exchanger @ 40 psi has cut a hole into the heat exchanger. My question is does velocity have any part in this? Someone had told me that do to the size of the boiler (2,000,000 BTU) and the size of the pipe feeding the heat exchanger, the velocity of the of the steam is higher and therefore creating a hole in the heat exchanger. Is there a formula to figure this or can anyone just explain it to me. Thank you--Rick
 
Engineering news on Phys.org
No, the BTU rating has very little to do with the pressure/velocity of the steam in the system (ie, a vastly oversized boiler would simply fire less often and produce roughly the same pressure/velocity). What you have there is probably due to corrosion.

Where is the hole, exactly? I'm pretty sure that copper and steel are the metals that don't work-and-play-well-with-others in plumbing. Ie, if you put them near each other without a dielectric fitting to separate them, they will create a galvanic cell and quickly dissolve the steel.
 
Last edited:
It could very well be an erosion issue. Usually a heat exchanger won't be made entirely out of copper, just the core. Where exactly is the hole in the heat exchanger? Does it happen at a 90° bend? I am imagining a shell and tube heat exchanger. Is this correct?
 
Thread 'I need a concave mirror with a focal length length of 150 feet'
I need to cut down a 3 year old dead tree from top down so tree causes no damage with small pieces falling. I need a mirror with a focal length of 150 ft. 12" diameter to 36" diameter will work good but I can't think of any easy way to build it. Nothing like this for sale on Ebay. I have a 30" Fresnel lens that I use to burn stumps it works great. Tree service wants $2000.
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...
Thread 'Where is my curb stop?'
My water meter is submerged under water for about 95% of the year. Today I took a photograph of the inside of my water meter box because today is one of the rare days that my water meter is not submerged in water. Here is the photograph that I took of my water meter with the cover on: Here is a photograph I took of my water meter with the cover off: I edited the photograph to draw a red circle around a knob on my water meter. Is that knob that I drew a red circle around my meter...

Similar threads

Back
Top