The discussion centers on addressing power swings in an industrial power system featuring a gas turbine generator and a step-up transformer. Operators report significant power swings, particularly following severe earth faults. Potential causes identified include excessive series impedance between the generator and load, exciter dynamics, and speed governor or prime mover dynamics. Participants emphasize the need for more detailed information, such as the duration of the swings, to provide effective solutions. Overall, addressing these factors is crucial for stabilizing the electrical system.
m.s.j
Messages
212
Reaction score
1
An industrial power system includes one gas turbine generator (6KV, 12 MW), a step up transformer (6/20 KV, Dyn11, 20 MVA) and relevant distribution system. The 20 KV side of power transformer is earthed by a low impedance neutral grounding resistor. The rated current of resistor is 250 A for 10 seconds.
According to operator's electrical reports, some times badly power swing occurs in electrical system especially after one sever Earth fault.

What is your opinion? How can we solve this problem?



--------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
m.s.j said:
An industrial power system includes one gas turbine generator (6KV, 12 MW), a step up transformer (6/20 KV, Dyn11, 20 MVA) and relevant distribution system. The 20 KV side of power transformer is earthed by a low impedance neutral grounding resistor. The rated current of resistor is 250 A for 10 seconds.
According to operator's electrical reports, some times badly power swing occurs in electrical system especially after one sever Earth fault.

What is your opinion? How can we solve this problem?
--------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
First, you don't provide enough information for a real answer. You don't even give us the periods of those swings.

But excessive swings can be caused by:
  • too much series impedance between generator and load
  • exciter dynamics
  • speed governor/primer mover dynamics
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...