The number of heat exchangers in series

  • Thread starter Thread starter cayusbonus
  • Start date Start date
  • Tags Tags
    Heat Series
AI Thread Summary
To design a system of heat exchangers in series, it's essential to calculate the effectiveness, heat capacity ratio, and overall heat transfer coefficient using the E-NTU method. The number of heat exchangers needed can be determined through empirical conditions and graphical techniques found in the Heat Exchanger Design Handbook. Modern tools like Engineer Equation Solver (EES) can simplify this process by treating multiple heat exchangers in series as a single unit with increased shell passes. While increasing the number of exchangers can improve the F factor, the gains diminish as the number increases. Ultimately, a balance must be struck between the number of heat exchangers and their efficiency.
cayusbonus
Messages
2
Reaction score
0
Hi, I need to design a system of heat exchangers for a steady-state process. I have inlet temperatures of the fluids, the amount of heat that must be exchanged, the max flow ratio and other data. The objective is to reach the exchange area and the length of the shell. My problem is that I have not idea about how many heat exchangers I must put in series, Better said, I don't know how the number of heat exchangers in series afect to the areas and the lenghts, when all the heat exchangers must be the same. The heat exhcanger must have one shell pass and two tubes pass.

Thanks.
 
Engineering news on Phys.org
Since you have the inlet tempreture and all the fluid properties you can calculate the effictiveness of the heat exchanger where E=q/qmax
and then calculate the heat capacity ratio Cr
And the overall heat transfer coefficient U
Then by using E-NTU method u will have NTU=UA/Cmin
where NTU can be calculated from tables or the figures you can find those at "Fundamentals of Heat and Mass Transfer-Incropera" at chapter 11 section 4
 
Last edited by a moderator:
Black-Mind said:
Since you have the inlet tempreture and all the fluid properties you can calculate the effictiveness of the heat exchanger where E=q/qmax
and then calculate the heat capacity ratio Cr
And the overall heat transfer coefficient U
Then by using E-NTU method u will have NTU=UA/Cmin
where NTU can be calculated from tables or the figures you can find those at "Fundamentals of Heat and Mass Transfer-Incropera" at chapter 11 section 4

Ok, I had find a solution for this.

Your mean will run if you've only one heat exchager. The problem here is that we've not the number of heat exchanger of shell&tube class in series needed, and this number must be fixed. So, one method can be readed in the Heat Exchanger Design Handbook p.272 Chapter 5. This text give you an empirical condition that determines if more than a self heat exchanger is needed, and one graphical technique for estimate this number.

heatex-1.jpg

But nowadays we have a powerful computers and good tools that allow us to improve this results. For example, with EES (Engineer Equation Solver) you can stablish this number reasoning that X heat exchangers in series are like one heat exchanger with X shell passes. Then, you can use the shell&tube routines increasing the 'N' number (shell passes), obtaining the F factor (or epsilon, depending on the method). You can do this with tables and graphical representations of F, epsilon etc. but is a really heavy work.

In conclussion, with the graphical technique you achieve the number of heat exchangers for a F=0,8, but increasing X, you can rise F, but with a negative exp. behavioring (the F changes are lesser when X rises).
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top