Three single phase transformer with different %Z's

AI Thread Summary
The discussion revolves around calculating line currents in a three-phase circuit with a transformer bank made of three single-phase transformers, two with 5.35% impedance and one with 4.04%. The user seeks to understand how differing transformer impedances affect line currents, particularly in relation to current imbalances causing issues with VFDs and soft starts. Basic circuit analysis is suggested as a method to solve the problem, with a focus on the relationship between phase currents and line currents. The conversation highlights the importance of recognizing that each line current is the sum of the two phase currents it connects to. Overall, the discussion emphasizes the need for straightforward analysis in understanding the impact of transformer impedance on current distribution.
JWT
Messages
4
Reaction score
1
Hello everyone,

I have a three phase circuit that consists of a three-phase transformer bank feeding a balanced three-phase delta load. The transformer bank consists of three single phase transformers connected in delta. Each transformer is rated at 333kVA, 2400V. Two of the transformers have percent impedances of 5.35%, while the third has a percent impedance of 4.04%. Also, each transformer has the same X/R ratio of 4.5 (if that matters), and assume the balanced load is 0 ohms, and the line impedance is 0 ohms.

My question- in this circuit, how would you calculate the three line currents?

I appreciate your time.
 
Engineering news on Phys.org
By the way, this is not a homework question. I just want to see the effects of difference in transformer impedances on the line currents, even if there are nothing but three-phase loads in the facility. VFD's and soft starts are tripping on current imbalance.
 
JWT said:
and assume the balanced load is 0 ohms, and the line impedance is 0 ohms.

So you're after short circuit currents?
 
In this example, yes. Really what I'm after is getting an idea of what the percentage deviation would be on the line currents if a three-phase delta secondary comprised of single phase transformers that had different percent impedances (which in my case, two cans have 5.35%Z while the third has 4.04%Z).

Thank you, sir, for your help.
 
i didn't set down with pencil and paper

but does this not look soluble by basic circuit analysis?

3ph.jpg

Shorting the 3 apexes sets each phase current trivially to V/Z ,
is each line current not the sum of the two phases to which it's attached ?
 
Yes, sir. That does make sense. For some reason I was looking into using sequence impedances and didn't think to just do a simple nodal analysis. Thanks again for your help.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...