Transformer short circuit fault calculation clarification

AI Thread Summary
The discussion focuses on performing a short circuit fault calculation for a transformer during a three-phase bolted short circuit. The transformer specifications include a 5% impedance and a cable impedance of 0.00306 + j0.0027. The calculation for fault current at the load uses phase voltage, as it corresponds to the voltage drop from the neutral point of the WYE transformer to one phase. This approach aligns with the winding impedance, making it suitable for a star connection. Using phase voltage simplifies the calculation and maintains consistency with the transformer’s secondary winding.
lavalin
Messages
7
Reaction score
0
Hi,

I'm trying to perform a short circuit fault calculation on this transformer and load I have when a 3 phase bolted short (worse case) occurs.

The transformer specs are below:
Z(transformer)=5%, Z(cable)= .00306 + j.0027, Delta/Star 6.6kV/400V

I can understand calculating the short circuit available current at the load:
Ifault(load) = Vphase/Z(transformer)
where Z(transformer) is the impedance of one winding, and the voltage across it would be 400/1.73 ~=230V
Ifault(load) = 230/.05
= 4.6kA

Now calculating the fault down at the load is where I get a little confused:
The example I'm following states that the load current fault for a 3 phase bolted short is:
Ifault(load) = Vphase/(Z(transformer) + Z(cable))

My only guess/understanding of why they use Vphase is that Vphase represents the voltage drop from the neutral (mid point) of the WYE transformer to the end of 1 phase? I've drawn a diagram to help clarify what I mean, its hosted at:
http://img83.imageshack.us/my.php?image=61884112bb8.jpg

Can someone please explain to me why they use Vphase in the load fault calculation?
 
Engineering news on Phys.org
If = Vph / Ztr(ohm)

Ztr(ohm) = %Z / Zb

Zb = V2/S

%Z : Transformer per unit impedance
V : Transformer Rated voltage (V)
S : Transformer Rated power (VA) :smile:


--------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Thanks for your reply. My question was however clarification on why they use phase voltage when they're calculating at the load end, total fault current that the transformer can deliver.
 
Hi! I would say:

They use the phase voltage because this fits with the winding impedance, and the load is in star connection as well. This gives you the current in a secondary winding.

Within this logic, you could equally well compute everything with line voltages and equivalent delta connections. It would be consistent, but less direct and less usable.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back