In calculating base values for current and impedance in polyphase AC circuits, particularly 3-phase systems, the line-to-line voltage is typically used as the base voltage. The base power is taken as the total 3-phase power, while the line current is derived from the relationship I = S / (sqrt(3) * V). This approach allows for consistent calculations of impedance, assuming it is connected in a star configuration. Understanding the distinction between line-to-line and phase voltage is crucial for accurate base value calculations. Proper selection of base quantities ensures accurate analysis and design in electrical systems.
anon6912
Messages
21
Reaction score
3
When calculating base values for current, impedance etc
do we use the line to line voltage or the phase voltage?

What's the reason for using one over the other?
 
Engineering news on Phys.org
What is a "line to the line voltage"? What is "phase voltage"? I don't understand your question.
 
My best guess is that he's asking about polyphase AC circuits, likely 3-phase.

I don't know much about 3-phase though.
 
If you are talking about per-unit system, this is the usual practicce.
Take Total 3-phase power S, as base power,
Take Line-to-Line voltage V, as base Voltage V.
Take Line-Current I, as base Current
Take an Impedance Z, as base impedance

But since you can only select two Base quantities independently, If you say take S and V as the initial base quantities (which is the usual practice) then
I = S / sqrt(3)*V

Now, the Impedance Z is assumed to be that impedance Z, which when connected in Star fashion in a 3 phase line with line-to-line voltage *V* will result in line Current *I*.

So, I hope that now you can find the base impedance Z, from the base voltage V and base Power S.
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...

Similar threads

Back
Top