What is the Short Circuit Capacity for a 24 kW 3-Phase Generator?

Click For Summary

Discussion Overview

The discussion revolves around determining the short circuit capacity for a 24 kW 3-phase generator, specifically focusing on the available short circuit amps and the %Z rating. Participants explore the implications of short circuit conditions, the importance of understanding the maximum current flow during such events, and the necessary ratings for breakers to handle potential short circuit currents.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant seeks information on the short circuit amps and %Z rating for a 24 kW generator, indicating difficulty in finding relevant charts.
  • Another participant suggests using the formula p=iv to find maximum current but admits uncertainty about calculating short-circuit draw and recommends measuring coil resistance.
  • A participant emphasizes the significance of knowing the short circuit current, explaining that it can exceed the regular amperage rating and poses risks if breakers are not rated for such currents.
  • There is a discussion about the inductive nature of the generator, noting that resistance alone is insufficient for calculations, especially as inductance can vary with operational conditions.
  • One participant suggests contacting breaker manufacturers for guidance on appropriate interrupting ratings for the generator's short circuit capacity.
  • Concerns are raised about the ampacity of cabling in relation to short circuit conditions, with speculation that components may fail under high current spikes.

Areas of Agreement / Disagreement

Participants express varying levels of understanding and experience regarding the short circuit capacity of generators. There is no consensus on how to accurately determine the short circuit amps or the appropriate ratings for breakers, indicating ongoing uncertainty and differing viewpoints.

Contextual Notes

Participants mention the need for specific measurements and considerations regarding inductance and resistance, as well as the potential for significant current spikes during short circuits. The discussion highlights the complexity of accurately assessing short circuit conditions in generators.

Josh111
Messages
37
Reaction score
0
I have a 24 KW 3 phase 120/208 volt synchronous generator I bought from China and I am having trouble finding the available short circuit amps or the %Z rating. Is there a chart anyone is aware of for common short circuit capacities?
 
Engineering news on Phys.org
Hint: p=iv

EDIT: This usually just gives you the maximum current you're able to draw at roughly the nominal output voltage. How to figure out the short-circuit draw, I have no idea. But you could start by finding the coil resistance (if this is possible--it's probably too low to measure with your standard household multimeter). If you're worried what might happen when you have a short, you should probably get a small breaker panel, or an appropriate in-line fuse.
 
Last edited:
I am aware of this but what I need is the short circuit amps amps

I need to know the amperage that will flow in the event of a short circuit. Every power source has a impedance. This and the applied voltage determines the maximum current flow when there is a short.( this is not the regular amperage rating of the power source but much greater)

The reason this is important to know is because when a short circuit occurs, the maximum current (much greater than rated current of power source or the breaker trip rating) flows for a short moment before the breaker trips. (Usually about 3/60 second)

The danger is that if the breaker is not rated to withstand the short curcuit current of the power source, it may explode!

Considering the above it is necessary for breakers on a system to be able to withstand the short circuit current. The maximum short circuit current a breaker may withstand is called the "interrupting rating" in the USA. A common interrupting rating in USA for breakers in smaller systems is 10000 amps. Many breakers say:" interrupting rating 10000 amps" or "suitable for use on a circuit capable of delivering not more than 10000" amps. Larger systems require higher ratings which are commonly available. This should not be confused with the breaker's trip amps.
 
MATLABdude said:
Hint: p=iv

EDIT: This usually just gives you the maximum current you're able to draw at roughly the nominal output voltage. How to figure out the short-circuit draw, I have no idea. But you could start by finding the coil resistance (if this is possible--it's probably too low to measure with your standard household multimeter). If you're worried what might happen when you have a short, you should probably get a small breaker panel, or an appropriate in-line fuse.

It is not enough to know the resistance because the source is also inductive. With something stationary like a transformer it may be possible to find the inductance in henrys but with a motor inductance decreases when RPM increase( thus a motor draws more current at startup than at rated speed.
 
Josh111 said:
It is not enough to know the resistance because the source is also inductive. With something stationary like a transformer it may be possible to find the inductance in henrys but with a motor inductance decreases when RPM increase( thus a motor draws more current at startup than at rated speed.

That's true; however, you know that the inductance will only increase (usually slightly) the coil impedance. 24 kW is a building-suitable backup generator, and unfortunately, this is far outside my experience. However, since this sort of things *is* done quite frequently, you can probably contact Siemens, Square-D or whomever is your favourite fuse / breaker manufacturer and ask them what an appropriate interrupter would be.

Although you're probably feeding with 3/0 or 4/0 cabling, ampacity (with any given temperature-rated insulation) is only for continuous current, and I have no idea whether it'd hold up with 10 or 15 kA spikes (these looks like standardish household interrupting capacity). I have a feeling that whatever is causing the short--or the generator windings themselves--will vapourize in such a case.

Good luck; hopefully someone else more knowledgeable can weigh in on this.
 

Similar threads

  • · Replies 77 ·
3
Replies
77
Views
9K
  • · Replies 17 ·
Replies
17
Views
4K
  • · Replies 42 ·
2
Replies
42
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
9
Views
2K
Replies
10
Views
3K
Replies
12
Views
8K
Replies
9
Views
8K
  • · Replies 7 ·
Replies
7
Views
5K
Replies
1
Views
3K