3 Phase Systems in a Wye Configuration

AI Thread Summary
In a balanced wye configuration, the neutral point maintains a zero voltage potential, and the line-to-line voltages remain sinusoidal and symmetrical, separated by 120 degrees. As one phase voltage changes, the other two adjust accordingly to ensure that the sum of the phase voltages equals zero. If the system is unbalanced, it can occur due to different peak voltages, phase angles not being 120 degrees apart, or varying loads. When a load is disconnected, the impedance becomes infinite, leading to unbalanced currents, but the total current in the system will still sum to zero. Proper load balancing is essential for the neutral conductor to carry no current.
jendrix
Messages
120
Reaction score
4
Hello,

I have been going over the above topic and have a question about the neutral point of a balanced wye configuration. Would the line to line voltage remain constant? I am trying to picture two sine waves 120° apart and it's making me think the Va would be reducing as Vb was increasing at certain points? So would Vline still be alternating sinosoidally?

The reason I ask is I did an experiment in class where we had to set the line voltage to 10V and confirm it with a multimeter. Is it possible the multimeter was showing the peak value?

On another note, am I correct in thinking the voltage potential at the neutral point would be zero provided the system was balanced?

Thanks
 
Last edited:
Engineering news on Phys.org
You are correct in your thinking that, if the system is balanced, the neutral potential would be zero.

You are also correct in your thinking that, as one of the phase to neutral voltages changes, the other two will also change such that Va + Vb + Vc = 0. The line to line voltages would also be sinusoidal.
 
magoo said:
You are correct in your thinking that, if the system is balanced, the neutral potential would be zero.

You are also correct in your thinking that, as one of the phase to neutral voltages changes, the other two will also change such that Va + Vb + Vc = 0. The line to line voltages would also be sinusoidal.

So that would mean the current Ia, Ib and Ic have a phase different with each other but at all times the sum of current at the neutral node would be 0?

Therefore in order for a system to be unbalanced the input voltage at A,B,C would either have to have a different peak or not be 120 degrees apart? Or have different loads?Thanks
 
jendrix said:
So would Vline still be alternating sinosoidally?

Yes. The differential voltage between two phases is sinusoidal.

The line voltages will be symmetrical and separated by 120° about the neutral.

The current will be balanced if the load is balanced. The phase of the current will be determined by the impedance of the load.

If the load is not connected to the neutral then the neutral currents will cancel at the centre of the 'Y' and the neutral conductor will carry zero current.

See attached picture. It shows 3 phases, each 230Vpeak, NOT RMS.
It also shows one of the three, two phase differential line voltages, red – yellow.
3PH.png
 
Baluncore said:
Yes. The differential voltage between two phases is sinusoidal.The current will be balanced if the load is balanced. The phase of the current will be determined by the impedance of the load.

If the load is not connected to the neutral then the neutral currents will cancel at the centre of the 'Y' and the neutral conductor will carry zero current.

View attachment 203303

If the load at for example A wasn't connected then wouldn't that cause the system to become unbalanced as the the impedance at A would be infinite as it would be an open circuit?
 
jendrix said:
If the load at for example A wasn't connected then wouldn't that cause the system to become unbalanced as the the impedance at A would be infinite as it would be an open circuit?
Baluncore said:
The current will be balanced if the load is balanced.
If the load is unbalanced then the currents in the lines will be unbalanced.
If one line is disconnected, the total current flowing in the three lines will still sum to zero. There can be no neutral current.
The load may not function correctly if one phase is not connected.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top