Purpose of 220Ω Resistor in Digital Input Circuit - Dan
The 220Ω resistor in the digital input circuit serves as a current limiter for the opto-coupler LED, preventing excessive current draw that could damage the device. When the switch is closed, the voltage across the contacts is less than 24V due to this resistor, making the input configuration valid as a 24V digital system. The resistor also ensures that the voltage rating of the opto-coupler is not exceeded. The discussion emphasizes that while the circuit can handle 24V, the actual voltage at the switch will vary based on the circuit's configuration. Understanding these details is important for proper wiring and system functionality.
fonz
Please see attached schematic.
Basically the diagram shows a single channel of a 32-channel digital input card for an industrial controller.
My diagram represents this configuration with the 24V supply externally sourced to terminals 65 & 66.
The question is what is the purpose of the 220Ω resistor?
Also, the voltage between the switch (the input) and ground is less than 24V because of this resistor. So calling it a 24VDC input is not strictly true am I right?
Finally, I am assuming the unlabelled resistor in my diagram has two purposes:
1. a current limiter for the LED
2. a pullup resistor for the logic circuit
Am I correct?
Thanks
Dan
The 220 is a Current Limiting resistor - consider all of the inputs are closed at once, the draw on the Power Supply will be too high, the extra resistor on the opto-coupler LED - limits the current for that device, the opto may also be rated for different voltage.
When the external contact ( Customer Wiring) is open, there will be a full 24V there. As a digital 24 V system this is valid - when the switch closes, you will not have 24 V across the contacts.
All you need to worry about is the Customer Contact - the internal diagram is for reference, for example if you were using solid-state contact ( line NPN) it shows how to be connected.
I thought the resistor R was to limit the current for the opto-coupler LED? Assuming this is the case are you also saying the the 220 resistor is to make sure the voltage rating of that device is not exceeded as well as limit the current drawn from the supply?
With regards to the Voltage AB, I get what you are saying about the open circuit voltage being 24V, but is my formula correct for the closed circuit voltage? (again, assuming no volt drop across the opto-coupler).
I realize these questions are unnecessary for just simply wiring the card up but I'd like to know the full details anyway just for reference.
Thanks for helping
When the switch is closed the voltage at the switch is between 0 and 24 V --- it is a 24V Digital Input Card - the inputs individually can not "take" 24 V INPUT - this is a standard way these cards are configured. The wiring, switches etc. that you use need to be 24V or greater.
Can I draw your attention to the sketch on the second page of the PDF? I appreciate that it's a 24VDC input card and by externally powering the inputs I do agree the voltage across the input terminals will be 24V however in my configuration I am connecting the 'internal 24V supply' to the 'external 24V supply' which according to the manual is acceptable.
Thus you end up with a circuit as shown in my sketch. In which case the 24V is dropped across the 220 resistor and when the circuit is closed, is split between 220 and R.
Sorry I did not make this clear, my intention is to use the internal 24VDC supply by linking the terminals.
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...