Flow rate calculation of hydrogen gas in case of leak

In summary: There is a hydrogen leak. If you are trying to determine the flow rate of the gas, shutting down the hood and making a calculation will probably not be enough information. You will need to determine the concentration of hydrogen in the air, and the rate at which it is leaking. It is important to note that the concentration of hydrogen will be different at different distances from the leak. The rate of the gas leak will also be affected by many factors, including the size of the opening, the type of material in the line, and the pressure of the gas. It is important to contact a professional engineer to help with these calculations. 3) The safe use of hydrogen. In
  • #1
Zion309
8
4
Hi. I'm a mechanical engineer, but working as Safety Engineer. I have a question how to calculate the flow rate of hydrogen gas before a flow controller in case of leak through a 4.5 mm line at 35 bar pressure. Thanks in advance.
 
Engineering news on Phys.org
  • #2
What will the result of this calculation be used for?
 
  • Like
Likes Zion309 and berkeman
  • #3
Thread closed temporarily for Moderation...
 
  • Like
Likes Zion309
  • #4
Zion309 said:
Hi. I'm a mechanical engineer, but working as Safety Engineer. I have a question how to calculate the flow rate of hydrogen gas before a flow controller in case of leak through a 4.5 mm line at 35 bar pressure. Thanks in advance.
Welcome to the PF.

Your post is a bit worrisome. Your Profile page shows that you have a BSME, but you are needing to ask on a web forum how to do a basic gas flow rate calculation? Did they not cover that in your undergrad ME classes?

And in your country, are there not Professional Engineer exams and qualifications/certificates for the position of Safety Engineer? Since your work sounds like it could affect the life safety of your coworkers, it would seem that such a PE certification would be a routine requirement...

ChemAir said:
What will the result of this calculation be used for?
And what he said...
 
  • #5
ChemAir said:
What will the result of this calculation be used for?
To verify if the walkin fumehood is capable to exhaust the hydrogen gas in case of leak. Thank you.
 
  • #6
Zion309 said:
To verify if the walkin fumehood is capable to exhaust the hydrogen gas in case of leak. Thank you.
In addition to @berkeman comments, and @ChemAir, it would seem that your question is perhaps not quite complete.
It is a bit too terse what you are trying to accomplish.
Have a sit down, and write down on paper what would be, or could be, the problems associated with a gas leak.
Are there standard regulations to follow?
Why have you been assigned this task. From whom? Plant supervisor? Lab supervisor? ??
what do they want, and have asked you to do?
Maybe you already know, and are assuming others know also.
You might be more interested in the fumehood capability calculations, and resulting air mixtures surrounding the leak.
Are you interested in asphyxiation, explosive gas mixtures, maybe something else?
With a full blown hose rupture, what are procedures to evacuate the area, or maybe even the building? would that even be necessary?
Who contacts emergency responders? Is that necessary?
How much hydrogen on site?
Like, how far down the line are you supposed to go with this.

I know nothing about nothing about nothing here, but even so, these contemplative points do come to mind.
How far have you progressed so far.
 
  • Like
Likes Zion309 and berkeman
  • #7
Project tasks that include "life safety" and involve safety systems, controls, interlocks, alarms, etc., can be a pretty complicated field to navigate, and small problems (Can my hood remove all the hydrogen that could leak out?) can't be considered in a vacuum.

Some things worth considering, some redundancy to @256bits thoughts :
-What was the original design basis for the hood? Is the design adequate for use before adding a hydrogen leak to its capabilities? Is the hood design suitable for the presence of significant amounts of hydrogen (no ignition sources)? Is the hood configuration such that it is unlikely to trap hydrogen in places?
-Does this hood have other uses at the same time?
-Is it normally occupied by person(s), and what level of PPE do they wear?
-Are there hydrogen leak detectors in the hood? Should there be? What type? Calibrated how frequently?
-If the power to the lab shuts off, what happens to the hydrogen/hood system?
-What is the source of the hydrogen? Is it large enough to fill the room (or the building) if the hood stops working? Could the leak cause the hydrogen source some type of problem?
-Should there be an interlock/shutdown when a leak is detected? What all, specifically should be shut down? What order should they be shut down? When I do this, does this cause any other new problems that weren't there before? Are there other chemicals, reactions, testing in the same vicinity that could have incompatible materials present?
-Will there be preventive maintenance to verify the hood performs as it should?
-Will this require re-training of affected personnel?

While some concerns seem a little excessive, others probably are not, and you should be considering the larger picture, weighing things appropriately.

Here in the US, I would encourage someone who is out of their element on these issues to look into the following:
1) Contact the supplier of the hydrogen. Manufacturers under the Responsible Care standard will provide some degree of guidance, training, etc. on the safe use of their chemicals. This guidance could include auditing an installation or an installation plan. A hydrogen supplier will be current on SDS and engineering controls technology. This is likely to be your best resource if they are a large supplier. If your current supplier can't provide this, it may be worth considering an alternate, if possible.
2) Contact someone at your company or institution who is responsible for questions about insured risk. There is usually an insurance representative/agent/inspector that could provide guidance. They will have a stake in bringing in a new risk, as it could affect insurance requirements.

If these are unsuccessful, it may be time to call an engineering company that can bring some expertise.
 
  • Like
Likes 256bits, Zion309 and berkeman
  • #8
ChemAir said:
-What was the original design basis for the hood? Is the design adequate for use before adding a hydrogen leak to its capabilities? Is the hood design suitable for the presence of significant amounts of hydrogen (no ignition sources)? Is the hood configuration such that it is unlikely to trap hydrogen in places?
Yeah, intrinsically safe walk-in fume hoods do look to be available, but you probably need to be sure it is designed for that (switches, lights, blower, etc.). One example:

http://www.fume-hoods.net/walk-in-fume-hood.html?gclid=EAIaIQobChMIwquoy9qt2wIVl9lkCh2Yvg4BEAAYAyAAEgLIEvD_BwE

walkin-fume-hood.jpg
 

Attachments

  • walkin-fume-hood.jpg
    walkin-fume-hood.jpg
    13.1 KB · Views: 1,159
  • Like
Likes 256bits
  • #9
berkeman said:
Welcome to the PF.

Your post is a bit worrisome. Your Profile page shows that you have a BSME, but you are needing to ask on a web forum how to do a basic gas flow rate calculation? Did they not cover that in your undergrad ME classes?

And in your country, are there not Professional Engineer exams and qualifications/certificates for the position of Safety Engineer? Since your work sounds like it could affect the life safety of your coworkers, it would seem that such a PE certification would be a routine requirement...And what he said...
Thanks for the comment. Would love to hear from you what formula to use wherein only line pressure and diameter is given.
 
  • #10
Zion309 said:
Thanks for the comment. Would love to hear from you what formula to use wherein only line pressure and diameter is given.
Do you understand the explosion risks and safety issues mentioned above by others?
 
  • #11
berkeman said:
Do you understand the explosion risks and safety issues mentioned above by others?
Sorry for not putting all the information which I admit is my mistake of not reading thoroughly the forum rules.
My inquiry is the result of Hazard Operability Study (HAZOP) conducted on bench scale reactor inside the walk-in fume hood.
HAZOP team raised a recommendation to verify if the fume hood is capable to vent the hydrogen in case of accidental leakage else, hydrogen detector will be installed outside the hood that will be connected to the Central Fire and Gas Detection System.
By the way, the walk-in fume hood is designed as per NFPA standard. Inspection frequency is done as per OSHA with current face velocity at 200 fpm.
It so happen that I came across this informative site.
Can you now please advice what formula to use?
 
  • Like
Likes 256bits
  • #12
Zion309 said:
Thanks for the comment. Would love to hear from you what formula to use wherein only line pressure and diameter is given.
In the profile question, there are no alternative answer in the dropdown list for "Education in Progress" and "Completed Educational Background".
 
  • #13
Zion309 said:
Hi. I'm a mechanical engineer, but working as Safety Engineer. I have a question how to calculate the flow rate of hydrogen gas before a flow controller in case of leak through a 4.5 mm line at 35 bar pressure. Thanks in advance.

I believe that you can use this calculator for that problem. https://www.pipeflowcalculations.com/gasleak/
 
  • Like
Likes Zion309
  • #14
Zion309 said:
By the way, the walk-in fume hood is designed as per NFPA standard. Inspection frequency is done as per OSHA with current face velocity at 200 fpm.
There are many NFPA standards. Is your hood approved as intrinsically safe and explosion proof?
 
  • Like
Likes 256bits
  • #15
The good thing about hydrogen is that being so light it will disperse more readily than other vapourized fuels.
That also makes it a bad thing as it can follow into nooks and cranies where other fuels will not, such as open pipes.
The bad thing about hydrogen is that an explosive mixture with air ranges from about 4% to 74 %., or rather flammability in air.

Being colorless and odourless hydrogen in the air is not detected by human senses.
A small electrical discharge can ignite the air-fuel mixture

See chart here, for comparison with a few other fuels:
https://www.energy.gov/eere/fuelcells/safety-codes-and-standards-basics
for dispersion coefficient in air, etc.

I do wonder how a leak rate can be correlated with the hazard within and around the hood.
Thing is to make sure there never( never say never ) is a leak, all connectors are standard for hydrogen, methods are followed.
Tanks are stored properly and connections are not forced.
If a leak, shutdown immediately.

I would say that safety protocol is a bunch lot more than leak rate, but should include everything from start to finish and followup for a safe work environment.
HAZOP should have knowledge, and educate all on the team.
Do they have a recommendation on reactor startup such as maximum leak rate before reactor startup = 0.
 
  • Like
Likes berkeman
  • #16
berkeman said:
There are many NFPA standards. Is your hood approved as intrinsically safe and explosion proof?
Hood Specification: NFPA 45 / ASHRAE 110 / ASTM E84 to comply with NEC / NFPA 70, Class I locations where flammable gasses or vapors may be present in the air in quantities sufficient to produce explosive or ignitable mixtures.
 
  • Like
Likes berkeman
  • #17
256bits said:
The good thing about hydrogen is that being so light it will disperse more readily than other vapourized fuels.
That also makes it a bad thing as it can follow into nooks and cranies where other fuels will not, such as open pipes.
The bad thing about hydrogen is that an explosive mixture with air ranges from about 4% to 74 %., or rather flammability in air.

Being colorless and odourless hydrogen in the air is not detected by human senses.
A small electrical discharge can ignite the air-fuel mixture

See chart here, for comparison with a few other fuels:
https://www.energy.gov/eere/fuelcells/safety-codes-and-standards-basics
for dispersion coefficient in air, etc.

I do wonder how a leak rate can be correlated with the hazard within and around the hood.
Thing is to make sure there never( never say never ) is a leak, all connectors are standard for hydrogen, methods are followed.
Tanks are stored properly and connections are not forced.
If a leak, shutdown immediately.

I would say that safety protocol is a bunch lot more than leak rate, but should include everything from start to finish and followup for a safe work environment.
HAZOP should have knowledge, and educate all on the team.
Do they have a recommendation on reactor startup such as maximum leak rate before reactor startup = 0.
Leak scenar
256bits said:
The good thing about hydrogen is that being so light it will disperse more readily than other vapourized fuels.
That also makes it a bad thing as it can follow into nooks and cranies where other fuels will not, such as open pipes.
The bad thing about hydrogen is that an explosive mixture with air ranges from about 4% to 74 %., or rather flammability in air.

Being colorless and odourless hydrogen in the air is not detected by human senses.
A small electrical discharge can ignite the air-fuel mixture

See chart here, for comparison with a few other fuels:
https://www.energy.gov/eere/fuelcells/safety-codes-and-standards-basics
for dispersion coefficient in air, etc.

I do wonder how a leak rate can be correlated with the hazard within and around the hood.
Thing is to make sure there never( never say never ) is a leak, all connectors are standard for hydrogen, methods are followed.
Tanks are stored properly and connections are not forced.
If a leak, shutdown immediately.

I would say that safety protocol is a bunch lot more than leak rate, but should include everything from start to finish and followup for a safe work environment.
HAZOP should have knowledge, and educate all on the team.
Do they have a recommendation on reactor startup such as maximum leak rate before reactor startup = 0.
I understand your concern. HAZOP study was done by a team of subject matter expert from research, technology, EHS including the designer of bench scale reactor.
 
  • #18
Problem solve through the use of gas dispersion modeling software. Sorry for creating this thread that goes nowhere.
Lesson learned: Lot of talks will not solve the problem.
Got more work to do.
Thanks
 
  • Like
Likes 256bits and berkeman

1. What is flow rate?

Flow rate refers to the amount of a substance that passes through a specific point in a given period of time. In the case of hydrogen gas leaks, it is the measurement of how much hydrogen gas is escaping from the leak per unit of time.

2. How is flow rate of hydrogen gas calculated in case of a leak?

The flow rate of hydrogen gas can be calculated by using the ideal gas law, which states that the volume of a gas is directly proportional to its temperature and pressure. By measuring the temperature and pressure of the leaking gas, the flow rate can be calculated using the formula Q=AP/RT, where Q is the flow rate, A is the area of the leak, P is the pressure, R is the gas constant, and T is the temperature.

3. What factors can affect the flow rate of hydrogen gas in a leak?

The flow rate of hydrogen gas in a leak can be affected by a variety of factors including the size of the leak, the pressure and temperature of the gas, the composition of the gas, and any obstructions or restrictions in the pathway of the gas.

4. What are the potential dangers of a hydrogen gas leak and its flow rate?

A hydrogen gas leak can be extremely dangerous, as hydrogen is highly flammable and can ignite at low concentrations. The flow rate of the gas can also contribute to the buildup of hydrogen in an area, increasing the risk of explosion or fire. In addition, hydrogen gas is also an asphyxiant and can displace oxygen in an enclosed space, leading to suffocation.

5. How can the flow rate of hydrogen gas in a leak be controlled or mitigated?

To control the flow rate of hydrogen gas in a leak, it is important to first identify and stop the source of the leak. This can be done by shutting off the gas supply or using specialized equipment to seal the leak. Additionally, proper ventilation and air flow can help to dissipate the gas and reduce the potential for ignition. It is important to always seek the assistance of trained professionals in the event of a hydrogen gas leak.

Similar threads

  • Materials and Chemical Engineering
Replies
1
Views
442
  • Materials and Chemical Engineering
Replies
18
Views
5K
  • Materials and Chemical Engineering
Replies
18
Views
9K
  • Materials and Chemical Engineering
Replies
3
Views
2K
  • Other Physics Topics
Replies
3
Views
1K
  • Materials and Chemical Engineering
Replies
9
Views
2K
  • Aerospace Engineering
Replies
10
Views
720
  • Mechanical Engineering
Replies
15
Views
1K
  • Materials and Chemical Engineering
Replies
6
Views
3K
Replies
9
Views
918
Back
Top