For a cold water dispenser project, standard heat transfer equations apply regardless of whether heat is being extracted or added, as "cold" is simply the absence of heat. The user is able to calculate the heat extraction needed to lower water temperature from 25°C to 0°C but struggles with the time calculation involving the aluminum container. To address this, it's essential to calculate the thermal resistance of the aluminum casing. Setting up a thermal-equivalent electrical circuit can help solve the transient heat transfer problem. Understanding these principles will aid in effectively designing the water dispenser.
kgmilano
Messages
2
Reaction score
0
good afternoon


i have a project to build a water dispenser. I'm strugling with heat transfer equations since it's cold that is being transfered. do i use the standard heat transfer equations even for cold? which equations do i use. water will be inside a 100x100x150 (1.5 litres) casing made out of aluminium.

thanks
 
Engineering news on Phys.org
Any heat transfer problem comes down to the transfer of heat. "Cold" is not a physical manifestation in heat transfer; there is only the absence of heat.

So yes, you use all the same equations.
 
thank you for the help. it's highly appreciated. I'm able to calculate the amount of heat to be exracted in order to decrease water from 25 deg to 0 deg and the time it takes. but i don't know how to calculate the time with the aluminuim as the container.
 
You'll have to calculate the thermal resistance of your aluminum container, and then set up a thermal-equivalent electrical circuit to solve the transient problem.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top