To calculate heat transfer through a multi-layer wall, the total heat transfer rate can be determined using the equation dQ/dt = (T1 - T2) / R, where R is the total thermal resistance of the wall layers. Each layer's resistance is calculated using R = L/(kA), with L being the thickness, k the thermal conductivity, and A the area. The intermediate temperatures between the layers can be found by assuming thermal equilibrium, where the heat transfer rates through each layer are equal. This approach allows for the calculation of the heat conducted through the wall without needing to find the exact temperatures at each interface. The discussion emphasizes the use of resistive networks to simplify the analysis of heat transfer in layered materials.
kris24tf
Messages
35
Reaction score
0
Hello, I have a test coming up and this is a question that will be on it...

The wall of a house is composed of solid concrete with outside brick veneer and is faced on the inside with fiberboard. The fiberboard width is 2 cm, the concrete width is 15 cm, and the brick width is 7 cm. If the outside T is -10 degrees, and the inside T is 20 degrees, how much E is conducted through the wall with dimensions 3.5mx5m in 1 hour?

I want to try something along the lines of k1A(T-T1)/d1=k2A(T2-T1)/d2 or something along those lines, but I know I have to use a T3, but I'm not sure how to find the third T. If you or anyone could help me set that up, that would be great.

I know to use the equation delta Q/ delta t= kAT/d but I also know I have to find the temperature between the brick and fiberboard. I just don't knwo how to find it. I've tried everything, so any clear guidance would save my day...
 
Physics news on Phys.org
I remember the the equation for a problem like this was something like..

power = [(area)(change in temp)]/[sumation of (length/conductivity)] , where the lengths are the thickness of each individual layer, and then the "conductivity" is the conductivity of that particular layer.

sorry, I'm kinda too tired to derive how they came about right now. I might do it later
 
Thanks, anytime before tomorrow at 11 would be great, but I appreciate that advice...

PS: I believe that answer is supposed to be 4.1 or something... I can't remember what,
 
Last edited:
This problem actually does not require you to find the temperature inbetween the conductive layers. We can make use of resistive networks. Also, we assume no convection effects at the surfaces.

\frac{dQ}{dt} = \frac{T_1 - T_2}{R}

where R represents the total resistance of the resistive network. We see here that because all the layers are in series (i.e. the heat must pass through all of them to get through to the other side), we can write:

R_t_o_t_a_l = R(concrete) + R(brick) + R(fiber)

If you recall, R = \frac{L}{kA}Now to also address your problem with finding the intermediate temperatures, you can do this through assuming equililbrium (dT/dt = 0) such that the heat through each suface is equal (or else there would be a temperature change and violate our assumed equilibrium).

You can write the equations of heat going through each and equivalate them, giving you enough equations to solve for the intermediate temperatures. For example:

\dot Q_1 = \frac{k_1A}{L}(T_1-T_2)
\dot Q_2 = \frac{k_2A}{L}(T_2-T_3)
\dot Q_3 = \frac{k_3A}{L}(T_3-T_4)

and so on, with

Q1 = Q2 = Q3 = ...
 
That last equation helped a lot! Thanks.
 
Kindly see the attached pdf. My attempt to solve it, is in it. I'm wondering if my solution is right. My idea is this: At any point of time, the ball may be assumed to be at an incline which is at an angle of θ(kindly see both the pics in the pdf file). The value of θ will continuously change and so will the value of friction. I'm not able to figure out, why my solution is wrong, if it is wrong .
Thread 'Voltmeter readings for this circuit with switches'
TL;DR Summary: I would like to know the voltmeter readings on the two resistors separately in the picture in the following cases , When one of the keys is closed When both of them are opened (Knowing that the battery has negligible internal resistance) My thoughts for the first case , one of them must be 12 volt while the other is 0 The second case we'll I think both voltmeter readings should be 12 volt since they are both parallel to the battery and they involve the key within what the...
Thread 'Trying to understand the logic behind adding vectors with an angle between them'
My initial calculation was to subtract V1 from V2 to show that from the perspective of the second aircraft the first one is -300km/h. So i checked with ChatGPT and it said I cant just subtract them because I have an angle between them. So I dont understand the reasoning of it. Like why should a velocity be dependent on an angle? I was thinking about how it would look like if the planes where parallel to each other, and then how it look like if one is turning away and I dont see it. Since...
Back
Top