How Do I Convert Voltage Readings to Pressure in mm H2O Using a Setra 264?

AI Thread Summary
To convert voltage readings from a Setra 264 to pressure in mm H2O, note that the instrument outputs a linear voltage signal between 0 and 5 VDC, corresponding to a pressure span indicated on the nameplate, typically ranging from 0.1 inwc to 100 inwc. For example, if the span is set to 100 inwc, 0 VDC equates to 0 inwc, 2.5 VDC to 50 inwc, and 5 VDC to 100 inwc. It's important to verify if a square root function is applied, especially if the instrument is used for flow rate measurements, although it may not be present in this case. Understanding the linear relationship between voltage and pressure is crucial for accurate conversions. Proper calibration and reference to the instrument's specifications will ensure accurate pressure readings.
temaire
Messages
275
Reaction score
0
I'm using a http://www.setra.com/ProductDetails/264_HVAC.htm" to measure pressure differences in a water manometer. However, I am getting outputs in voltage using a voltmeter and want to know how to convert these voltages to pressure in mm H2O.
 
Last edited by a moderator:
Engineering news on Phys.org
Your instrument will output a signal between 0 - 5 VDC.

The span may be between 0.1 inwc to 100 inwc. This should be listed on the nameplate.

The instrument will output the maximum span value at 5 VDC and linear values in between.

For example, suppose it is spanned to 100 inwc. The output will look like:

Instrument Output, Differential Pressure
0 VDC, 0 inwc
2.5 VDC, 50 inwc
5 VDC, 100 inwc

Sometimes, if a differential pressure instrument is used for flow rate, there will be a square root function included. Double check, but I did not see this.
 
I figured it out.

Thanks for the reply.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...