Understanding 3 Phase IEC Contactors/Starters
  • Thread starter Thread starter XPTPCREWX
    3 phase Phase
A 3-phase IEC contactor/starter is a high-current relay designed to control electric motors, allowing for their safe operation and starting. It complies with International Electrotechnical Commission standards, offering a modular design that can easily snap onto DIN rails for installation. Unlike NEMA starters, IEC starters are typically sold as components, allowing customization for specific applications. They are generally more compact and considered disposable below 100A, facilitating quick replacements. IEC contactors also adhere to Type 2 coordination standards for protection against short circuits, ensuring reliability in motor control applications.
XPTPCREWX
Can someone explain to me what a 3 phase IEC Contactor/starter is, how it works, and what its used for? Thanks
A contactor is basically a really high-current version of a relay:
http://en.wikipedia.org/wiki/Contactor
Suitable, for, say, handling the current required to start a motor. (Although some quick googling indicates that a contactor / starter, as manufactured by a number of companies, is a self-contained unit that allows you to engage the contactor).
IEC (International Electrotechnical Commission) is a standards body, similar to NEMA (National Electromechanical Manufacturers Association):
http://www.iec.ch/
http://www.nema.org/
So it's most likely a 3 pole single throw switch / relay (switches all three phases)
Thanks, for some reason I was thinking capacitor since it said starter.
The large number of IEC contactor sizes allows you to more closely match the contactor to the load or application. Unlike NEMA, where the available sizes are standard across the industry, the number of different contactor size ratings varies by manufacturer.
Generally, an IEC starter is about half the size of a comparable NEMA starter. Above 100A (NEMA Size 3), however, the physical differences between NEMA and IEC are negligible.
IEC products are more modular in nature; they can snap onto a 35-mm, or in larger sizes, a 75-mm DIN rail. This eliminates the need to drill holes and mount each component individually. Thus, putting them into a panel is relatively easy.
Unlike NEMA starters, which typically are sold fully assembled, IEC starters typically are sold as components (a contactor, an auxiliary block, an overload relay block) so that you can make your own assembly. You simply select the accessories needed for the application and snap them together, without the use of tools.
Also unlike NEMA starters, IEC-style thermal overload relays typically have fixed thermal elements, with an adjustment range that may require replacing the complete overload relay when significant motor FLC changes due to application requirements.
A large number of IEC contactors are applied in group installations, and NEC Sec. 430-53 deals with this application facet. However, this isn't unique to IEC contactors, since you can install any starter this way.
IEC products, more often than not, are sold to OEMs, which typically install them in applications where multiple devices are needed to control different functions of a machine.
Type 2 coordination is an IEC standard that can be applied to a NEMA-style product as well. Type 2 protection is afforded by the use of a properly rated and class of fuse with a contactor or starter. This type of protection requires that, after short-circuit condition testing, the contactor or starter must be reusable without component or part replacement. Also, no significant change is allowed in the operating time-current characteristics of the overload relay. This is a coordinated protection standard for the short-circuit protective device, contactor, and overload relay. The rules are the same for both IEC- and NEMA-style devices. For Type 2 coordination, the typical higher withstand rating of a NEMA-style starter provides a greater selection of short-circuit protective devices. Type 2 coordination with IEC-style products will offer the same coordination and degree of protection; however, the selection of fuse classes may be more limited. For short-circuit currents up to 5000A, Type 2 protection for IEC-rated motor starters would require Class RK5, J, RK1, or CC fuses. For short-circuit currents up to 100kA, Class RK1, J, and CC fuses are required.
Compared with NEMA-style products, IEC-style products are more disposable than serviceable. In fact, IEC products below 100A typically are considered disposable; they can be removed from a DIN rail, thrown away, and replaced with a new product in a matter of minutes.
Self protected starters represent a new category of combination starters as defined in UL 508-E. Typically, such a starter has a contactor, an overload relay, and short-circuit protection. The device also undergoes a unique testing procedure, one that goes beyond that for conventional combination motor controllers. This procedure tests the starter at different fault levels, verifying that coordinated protection similar to Type 2 is provided.
:wink:
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
Since I alluded to it earlier, and m.s.j. quoted them, the above is from an EC&M article:
http://ecmweb.com/mag/electric_differentiating_nema_iecstyle/
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...