From the descriptions in the accident analysis report, I get the impression that the SRVs talked about would be of a type which is called dual function direct acting valves. They are called dual function because they are able to be opened in two ways: a) automatically by the pressure reaching a set value (pressure mode), or b) by manual or remote actuation (actuation mode). They are called direct acting, because actuation operates directly on the valve body, not through an intermediate system.
I have attached a technical diagram of a dual function-direct acting valve cropped from
NRC report on SRV performance at US nuclear plants
In pressure mode, the valve would open automatically on exceeding the set point, which would in the case of Fukushima be around 7-8 MPa.
For manual or remote actuation, compressed air is needed to drive a pneumatic piston at the valve, and power is needed to open a valve that let compressed air flow to that piston. Then, the piston through a lever applies an opening force to the valve body, sufficient to open the valve -- on the condition that it can be assisted by an inlet steam pressure at or above about 0.7 MPa. If inlet pressure is below about 0.7 MPa. actuation will fail due to lack of opening force.
However, once successfully opened due to actuation -- (my question is, do I understand this correctly?) -- there would seem to be nothing that keeps the valve from closing except the pressure from the inlet steam. The piston-lever arrangement seems designed only to flip the valve open, not to keep it open. Once pressure falls below a certain level (about 0.3-0.4 MPa), the valve is meant to reseat, and to stay closed, and to open again only on actuation or by reaching its high pressure set point.
Attachments
Last edited: