Japan Earthquake: Nuclear Plants at Fukushima Daiichi
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #11,801
New Video Released By TEPCO - Radiation Measurement at Fukushima Daiichi
http://youtu.be/TAPsmgrGw30
  • #11,802
This
http://www.tepco.co.jp/nu/fukushima-np/images/handouts_111130_06-j.pdf
shows a diagram of corium flow. It is oddly specific.
EDIT: part of a big release of documents by TEPCO. I am surprised no-one except tsutsuji (thanks, again) is discussing it here, but it appears they now believe that they have core on the floor in all three reactors.
I wonder, how long they have been working under this assumption? Maybe as long as us?
  • #11,803
Speaking only for myself: I'm waiting for English translation.
It's interesting that (AFAIK) they did not tried to start the Core Spray (assuming there is a CSS) in U1. Maybe because they were already sure that there is nothing left there what can be cooled only by the Core Spray?
Ps.: I wonder if the state of the molten core on/in the containment bottom concrete was considered as a criteria regarding the recommended water level in the reactor building basements?
  • #11,804
  • #11,805
I'd still like to know how you get measurements from the bottom of the RPV if the core melted the bottom of the RPV out. All the wiring, the thermocouple junctions, everything would be vaporized. All those signals would report being "open circuit"
The thermal radiation alone would burn up all the wiring within 20+ feet just from being in proximity of the fuel. Not to mention the magnetically attached thermocouples would have all dropped off and be hanging by their wiring.
  • #11,806
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111202/0440_goninshiki.html Plant manager etc. were mistakenly believing that the isolation condenser was running. Tepco's internal investigation panel has completed its interim report. Concerning the fact that unit 1's isolation condenser was manually shutdown shortly after 6 PM on 11 March, the report says that the managers in the seismic-isolated building and in Tokyo were mistakenly believing that the isolation condenser was still running because a data saying that the water level was above fuel had been obtained from a water level gauge. As it is thought that the water level gauge, at that time, was not measuring the true value, it is possible that based on mistaken information, they held a mistaken awareness. Fuel started being uncovered 4 hours after the earthquake at around 7 PM at the earliest. According to the interim report, it is 8 hours after the earthquake, at around 11 PM that the managers began being aware of the possibility of fuel damage, after they grasped that radiation was rising.
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111202/index.html Tepco's internal investigation panel's interim report has been publicly released. It leaves many questions unanswered such as why huge quantities of radiation were released, and via which route they were released. The report does not depart much from what was previously said. The response to the accident is judged a number of times to have been "valid" or that "its direction was good". The cause of the accident is said to be "an unpredictable tsunami which entirely robbed safety functions". The report does not address the question of why Tepco did not immediately report to the government its own prediction, made 3 years earlier, of tsunamis higher than 10 m. Eight months after the accident, there is still an enigma concerning the operation of unit 1's cooling equipment, and concerning the route via which the radiation from unit 2, which is said to be the largest amount, was released.
http://www.tepco.co.jp/cc/press/11120203-j.html Tepco's internal investigation - interim report (Japanese)
  • #11,807
Are there any photos of the pressure vesel inside Fukushima reactor buildings (before accident)?
Also, how thick is the pressure vesel?
  • #11,808
tsutsuji said:
I translated the diagrams about unit 1 on pages 21, 22, and 27 of http://www.tepco.co.jp/nu/fukushima-np/images/handouts_111130_06-j.pdf
Thanks.
I could translate some parts of the documents by copying the text to the googletrans: really interesting, thanks for them.
One question. AFAIK as the fuel melts, some parts of it forms some solid crust around the liquid corium. Do anybody knows anything about the heat produced by the liquid corium and the crust, relative to the decay heat produced by the whole fuel assembly?
The analysis assumes that the whole fuel amount slumped down to the bottom of the containment: but the liquid part will escape on the first leak of the RPV, and only the crust will be left behind to erode the RPV further...
  • #11,809
Rive said:
Thanks.
If there is a crust, it would be metallic in composition, something like a steel foam with decay products mixed in. It would probably not be hot enough to do further damage, even if left uncooled
  • #11,810
Melting solids absorb heat (heat of fusion). The chemical reactions, e.g., oxidation of the Zircaloy would cause heat - probably on the order of decay heat.
The issue with corium, melted core, is that is increases the risk of breach of the pressure vessel, with an additional concern that if liquid metal falls into water, there will be a steam explosion.
  • #11,811
Sorry, I wasn't clear enough. I have to think it again.
So, as the core debris melting through the lower plenum and falling to the bottom of the RPV, the temperature there will ramp up: the slowly decreasing decay heat (and possibly other chemical heat sources) against the cooling effect of the RPV wall and the melting.
When the RPV wall breached, the liquid (and most hot) part of the core debris will immediately leave the RPV. This would create only a/some smaller leaks instead of cutting down the whole RPV bottom.
When this happens, the heat generated within the RPV will be reduced to the heat generated by the remaining crust, while the cooling will be ~ the same as before.
As the average temperature of the containment rises, the cooling of the RPV will decrease, so maybe all this will be iterated some times.
But at the end there must be an equation between the cooling by the RPV (around the melting point of iron) and he heat generation of the stuff still inside. After this equilibrium reached, there will be no more liquid corium leaving the RPV.
If the decay heat of the corium, and the RPV 'natural' cooling can be estimated then maybe we can give a number for the amount of hot stuff still inside U1 RPV.
  • #11,812
Can we therefore assume that there was no water in the PCV when the corium dropped. When water was later introduced, the corium would be cooled from the top and sides but not from the bottom. Why then did it not penetrate down further into the PCV?
  • #11,813
This information from TEPCO is based on modeling/simulation, not observations. Until they can physically check all such determinations will be educated guesses using the external observations (like radiation levels, composition of the emitted particles, sensor readings, etc) as inputs. The answer to your question "Why did it not penetrate down further..." is that no one really knows at this point where the corium is, except that there have not been steam explosions so far...
Still, many months after the accident, we don't know many many things and the accident scenarios put forth are best guesses based on the available (and incomplete) evidence.
  • #11,814
It would be helpful to have some idea of the scale of a possible corium steam explosion.
The current decay heat is less than 5 megawatts per reactor, afaik and there is water being injected at a steady pace, so at least the top of the corium is in water. That should limit any explosion.
A steam explosion would require the underside of the corium to reach new moisture and flash it into steam in a confined space, which seems to be a recipe for a corium burble rather than a massive explosion, unless I missing something important.
Has this eventuality been modeled in any public documents?
  • #11,815
It's the other way around. This is a scenario we are discussing. The scenario, being something of a worst-case, ASSUMES that there was no water. We don't know that to be the case (although it may be, at least for Unit 1, where the IC was off).
  • #11,816
I have translated the abstract at the top of http://www.tepco.co.jp/nu/fukushima-np/images/handouts_111130_09-j.pdf
Abstract
An estimate of Fukushima Daiichi units 1, 2 and 3's core status was publicly released on 23 May, and although cores in all three units were largely damaged and melted fuel had moved or fallen into the lower plenum, while not refuting the possibility that melted fuel had fallen ouside of the reactor pressure vessel, we estimated that most of it was being cooled in the vicinity of the lower plenum. The present public release consists of core status obtained by MAAP analysis and core status estimates based on core status evaluation that can be inferred from the behaviour of measured temperatures in every part of the plant.
Material for core status estimates were obtained by various operations, investigations, studies, and analysis performed since May. The estimates that were obtained are the following ones:
1) From the temperature behaviour of every part when injection rate is changed or when injection route is changed, it can be inferred regarding unit 1, as the RPV temperature decrease is large, that there are few fuel debris inside RPV, and regarding units 2 and 3, that fuel debris exist inside RPV.
2) As a result of calibration and of filling unit 1 and unit 2's water level gauges' reference tools with water, we can infer that a water level is not formed at the original fuel location inside the reactor, and that there is no fuel at the original location.
3) Conducting nuclear substance analysis of the gasses inside unit 1 and unit 2's primary containment vessels, we infer from cesium concentrations that fuel melted more at unit 1 than at unit 2.
4) Evaluating the heat balance of decay heat production and cooling, we estimate that the part of unit 1's decay heat that could not be cooled by the isolation condenser and by the high pressure core injection is about 3 times higher than that of units 2 and 3, and that this lead to early fuel and RPV damage.
5) From an estimate based on a RPV heat balance model, we infer that as of 10 October, at both units 2 and 3, the proportion of uncovered fuel is 3% or less, and that the fuel is largely submerged.
6) From an analysis concerning core-concrete reaction, we infer that even at unit 1, which is thought to contain the highest proportion of fallen fuel, the pedestal floor's erosion depth does not reach the PCV's inner wall.
Based on the above information and general analysis, it was possible to take further the estimations of core status we had performed in May. As a result, concerning unit 1, it can be thought that nearly all of the fuel that melted after the accident fell down into the lower plenum, and that there is almost no fuel left in its original reactor location. It can be thought that a great part of the debris that fell down into the lower plenum, fell down onto the primary containment vessel's pedestal. However, although the fuel debris create a core-concrete reaction, they were stopped due to the cooling performed by water injection and due to the decrease of decay heat, and we estimate that in the present situation, it remains inside the PCV where it is receives stable cooling. Concerning units 2 and 3, it can be thought that the fuel debris are for one part in the core's original territory, and for another part they have fallen into the lower plenum or onto the pedestal, and we estimate that in whichever place they might be, they are receiving stable cooling.
Nevertheless, far from observing directly into the reactor and into the primary containment vessel, this is a core status estimate based on various indirect informations and analysis, and in the future, using some methods, we want to grasp the situation through direct observation.
  • #11,817
Earthquake not a factor in Fukushima accident
http://www.world-nuclear-news.org/RS_Earthquake_not_a_factor_in_Fukushima_accident_0212111.html
02 December 2011
The tsunami of 11 March was the 'direct cause' of the accident at the Fukushima Daiichi nuclear power plant, concluded an official investigation report. It dismissed the idea that earthquake damage was a major factor in the accident.
A safe emergency shutdown was achieved within seconds of the magnitude 9.0 earthquake, said the Fukushima Nuclear Accident Investigation Commission composed of experts independent of plant owner Tokyo Electric Power Company. Control rods were fully inserted within seconds and all 13 diesel generators started as per design when tremors disconnected the grid connection. Instrumentation was working correctly, as were cooling systems.
Shaking recorded at the site was around the maximum that the plant was designed to cope with and still maintain nuclear safety but walk-down checks by plant staff showed no indication of significant damage to coolant systems.
I think this is premature.
Industry folks like myself are waiting to get a look inside before concluding what actually happened. Before that, we can only make some engineering/educated guesses/speculations based on external or indirect evidence. That means trying to piece together or make sense of the activity releases, the explosions, the visible damage, sounds reported by those onsite or by instrumentation, . . . .
IF the core melted, then what the instruments tell us about water levels, temperatures and pressures may not be accurate, or maybe some are, but others aren't. See the plots by Jorge Stolfi. One question then is - at what point during the event did the instrument readings become unreliable?
IF the core melted then there was essentially no cooling of the core, which essentially means no coolant in the core. The core may have melted - but at what temperature. Stainless steel melts at about 1450°C, Zircaloy-2 melts at 1800°C and the UO2 (+TU+fission products) melts at 2800°C. On the other hand, rapid oxidation of Zircaloy occurs at lower temperatures, so that could have reacted with whatever coolant was present and produced H2 + ZrO2, which is the source of the hydrogen. The cladding for these units is barrier cladding, which means it has Zr-Fe liner which can oxidize pretty rapidly at high temperature. Once the Zircaloy cladding fails, the fuel (UO2+fission products) is exposed, and at high temperature, the (M=U,Np,Pu,Am,Cm)O2 oxidize to higher order oxides M4O9, M3O8, and MO3, the latter of which is more soluble in water. The use of seawater, and the tsunamic flooding, complicated the scenarios regarding what happened with whatever contaminated coolant escaped. So some, or a lot, of fuel material and core could have simply chemically reacted and become an aqueous solution.
It's not yet clear at what temperature the melting occurred (IF any melting occurred) - anywhere between 1400°C and 2800°C, or perhaps slighly higher (that all depends on whether or not there was some level of heat transfer to the RPV and other structure via whatever fluid (aqueous solution, steam or gas) was present in the core).
One critical question: Was there coolant in the bottom of the RPV? That is where the control rod drive mechanisms/tubes reside. If the core melted, how did it manage to melt through the core support plate? If it did, then it had to displace any coolant present, while it melted the control rod drive mechanisms, as the then corium collected on the bottom of the RPV. Then it would have to had continue melting through the RPV (~ 5 inches or 127 mm), while melting the stainless steel guide tubes and the control rod drive mechanism (CRDMs).
Now the density of the corium is complex because it depends on the forms and proportions of melted material. Zircaloy-2 has a density of ~6500 kg/m3, stainless steel about ~8000 kg/m3, and UO2 about 10400 kg/m3 (water = 1000 kg/m3), so a molten mass can displace water.
Could the housing for the CRDMs have rupture during the earthquake? That's not clear, and TEPCO reported that the reactors scrammed. Could some other components or piping rupture during the earthquake, or during after shocks? Certainly any failure of the piping connected to the primary system would have made it difficult to get water to the core.
As for water under the RPV but in the PCV, that's not clear. If there was water present, but the rate at which a melted core dropped through the RPV was slow enough, there would not necessarily be a steam explosion.
Some useful data here (I know both authors) - http://www.ornl.gov/info/reports/1989/3445606042920.pdf
Assessment and management of ageing of major nuclear power plant components important to safety: Metal components of BWR containment systems
http://www-pub.iaea.org/MTCD/publications/PDF/te_1181_prn.pdf
Assessment and management of ageing of major nuclear power plant components important to safety: BWR pressure vessels.
http://www-pub.iaea.org/MTCD/publications/PDF/TE_1470_web.pdf
Integrity of Reactor Pressure Vessels in Nuclear Power Plants: Assessment of Irradiation
Embrittlement Effects in Reactor Pressure Vessel Steels
http://www-pub.iaea.org/MTCD/publications/PDF/Pub1382_web.pdf
http://nuclearsafety.info/ageing-management-and-long-term-operation/
The reactor pressure vessel (RPV) wall thicknesses for the BWR fleet were obtained from Reference 9, shown in Table 2-3. The maximum wall thickness is 7.125 inches (181 mm) and the minimum wall thickness is 4.47 inches (113.5 mm). The maximum vessel inner diameter is 254 inches (6.45 m) and the minimum vessel inner diameter is 185 inches (4.7 m).
The average wall thickness of the BWR fleet is 5.897 inches (150 mm). There is one vessel each at 4.47 inches (113.5 mm), 5.063 inches (128.6 mm) and 5.29 inches (134.4 mm). All other vessels are at 5.375 inches (137 mm) or thicker.
http://pbadupws.nrc.gov/docs/ML0906/ML090630402.pdf
9. BWR Vessel and Internal Project, BWRVIP-60-A, "Evaluation of Stress Corrosion Crack
Growth in Low Alloy Steel Vessel Materials in the BWR Environment," Technical Report
1008871, Electric Power Research Institute, Palo Alto, CA, June 2003.
BWRVIP-203NP: BWR Vessel and Internals Project
RPV Axial Weld Inspection Coverage Evaluation
EPRI 1016572 NP
Final Report, January 2009
  • #11,819
Excuse me for being unpolite, but what the hell is that supposed to mean? Granted, we don't have any clue what the situation inside the RPV really looks like.
But a few months ago TEPCO recalibrated the water level gauges of Unit 1 and discovered that, at that time, the water level was actually BELOW the bottom of the fuel. At the same time, temperature readings indicated that the fuel was sufficiently cooled, therefore well below its former position.
I'd like to read an explanation which describes how nearly all of the fuel could have relocated to the lower RPV plenum without melting.
There were times when we couldn't say for sure if there has "only" massive cladding damage or also melting occured. But those are long gone.
There is molten fuel in Fukushima. That's what I consider a fact.
  • #11,820
Not sure if melting is inherent in the core destruction process.
Presumably the fuel rod cladding could get oxidized and flake off before anything melts, with the fuel pellets falling down to collect on top of the core support plate.
That heap of fuel might then melt from the inside out and the melt would move as the TEPCO simulation suggests. Certainly it is hard to envision the fuel breaching the RPV without melting, although
I am fascinated by Astronucs comment that:
That is a novel idea, that the fuel might in fact have leached out to some extent. However, that should be detected by the water treatment process and nothing has even hinted at that afaik.
  • #11,821
I must add that they did the same thing for reactor 2 and there also water level is below bottom of the fuel rods.
  • #11,822
Zr fails at more than 700 C. Zr/H20 reaction is exotermic, so temperature quickly rose much higher after 700 C was reached. This also increases pressure, making it rather hard to pump cooling water into reactor in those conditions.
I don't see how anything "aqueous" could form under those conditions until corium melted through the bottom and thus pressure was released.
  • #11,823
These photos were captured Dec 1st here in the US. Interested to find out what was going on here
  • #11,824
02 December 2011
Yes, any conclusions at this stage should be considered very tentative. Especially as the latest core melt analysis features graphs which highlight a number of different instances where they cannot get the recorded data to match the results of their model analysis. For example the measured pressures quite early on at reactor 2 do not quite fit their models, which is why in past analysis they had to make assumptions about certain breaches/leaks in reactor and containment in order to make the model analysis results more closely match the recorded data. In the latest analysis documents its the one with filename ending in 6 that features such graphs for all 3 reactors and draws attention to periods of time where there are differences between the measured data and model results. Although we should note that back in May when NISA cross-checked TEPCOs analysis, they got some different results in places, but I think TEPCO still use their own analysis for the latest corium analysis, rather than using NISAs even though the NISA stuff does seem to make more sense in places. An example of this is that TEPCO don't have reactor 2's RPV failing until sometime on March 16th, but available data and other analysis tends to point to this happening earlier than TEPCO think. Due to the rather poor machine-translation of the corium melt stuff, I can't say how much this may have affected TEPCOs theories about status of core at reactor 2.
Certainly I do not have very many fixed and certain conclusions in my brain at this point. There are a few that we can be pretty certain about, such as certain extreme scenarios not having happened because there are not the very high radiation doses necessary at the site of the power station to support some of the more extreme 'reactor blew up and shot fuel everywhere' doom scenarios that a few people were very keen on in the first months. And am I correct to say that we can be reasonably sure that the reactors did SCRAM immediately after the earthquake, otherwise we would have seen much worse stuff unfolding as it would not only have been decay-heat that they had to deal with?
  • #11,825
The desalination 'evaporative condensation' equipment has leaked, allowing some water with 2.9Bq/cm3 Cs137 to head for a gutter.
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_02-e.pdf
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_01-e.pdf
And a description of the problem from the latest plant status (http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_03-e.pdf)
11:33 Workersfoundthattherewaspuddlewaterinsidethebarrieraroundtheevaporativecondensation
・12/4
apparatus (the estimated volume of water was approx.45 m3). At 11:52, stopped the apparatus.
12:14 Workers made visual inspection of the apparatus and thought that the leakage stopped. After that, conducted investigation. At 14:30, we found crack in the barrier made of concrete and water was leaking to the gutter (surface dose rate of leaked water: beta ray 110mSv/h, gamma ray 1.8mSv/h). We are considering emergency response to stop leakage of water to the outside of the barrier. In the meantime, water desalination apparatus is continuing operation. As we have sufficient volume of desalinated water, there is no impact on the Reactor water injection.
  • #11,826
I don't see anything interesting. What do you possibly think is interesting in these photos? They are out of focus or affected by weather conditions. The colours above reactor 2 building are from a crane, which can presently be seen very clearly on the live video. The orange colour to the right of reactor 3 building is probably a light. There is a light of a different colour in about the same place currently showing on the live video.
http://www.youtube.com/user/tbsnewsi#p/l/24eGVuK4G4M
I would have hoped people would have learned not to let their imaginations run wild over poor quality images by now.
  • #11,827
http://www3.nhk.or.jp/news/html/20111205/t10014402061000.html 45 tons of water have leaked from the desalinating facility. The leak was found at around 11 AM on 4 December. Cesium levels are brought to 45 Bq/cm³ but strontium levels are still high with 130,000 Bq/cm³. Tepco is checking if the water flew into the sea while putting sandbags in the downstream part of a 600 m long side ditch in which the water might flow before reaching the sea.
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_02-e.pdf "Leakage from evaporative condensation apparatus"
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_01-e.pdf "Fukushima Daiichi Nuclear Power Station Sampling result of leaked water from the evaporative condensation apparatus"
12/4 11:33 Workers found that there was puddle water inside the barrier around the evaporative condensation apparatus (the estimated volume of water was approx.45 m3). At 11:52, stopped the apparatus.
http://mainichi.jp/select/jiken/news/20111205ddm002040092000c.html Beta radiations due to strontium and other substances are between 100,000 Bq/cm³ and 1,000,000 Bq/cm³. The strontium concentration in the leaked water is about one million times as high as the standard set by the nuclear power regulating law for sea releases.The building's area is 30 m x 30 m. As the leaked water's height was about 5 cm, the leak's volume is 30 x 30 x 0.05 = 45 m³.
In all, as much as 220 tons of water may now have leaked from the facility, according to a report in the Asahi Shimbun newspaper that cited Tepco officials.
http://www.nytimes.com/2011/12/05/world/asia/more-leaks-from-fukushima-daiichi-nuclear-plant.html
  • #11,828
Thanks for the info, as TEPCO didn't mention the strontium in the documents about the leak I posted earlier.
In other news from the last week I see they found quite a lot more tritium in unit 1 sub-drain compared to unit 2, from samples taken mid-November.
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/111203e15.pdf
Also I see that the last line of an Asahi story about the recent core melt analysis sounds very much like what someone on this forum suggested a long time ago:
http://ajw.asahi.com/article/0311disaster/fukushima/AJ201112010004
TEPCO is considering the use of a special camera, resembling an endoscope, to monitor the interior of the reactors in the future.
  • #11,829
Is the source of the water specified, whether from the SFPs or the reactor building basements?
It would seem unlikely for the spent fuel pool water have such an elevated strontium content unless there has been significant damage to the stored fuel.
  • #11,830
tsutsuji
It wasn't clear to me from the earlier information http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111204_03-e.pdf how much water leaked. Was it 45 tons (seems a lot) or was it 0.45 tons (seems more likely)? The ambiguous phrase was "(the estimated volume of water was approx.45 m³)" where I don't know if the period belongs to the number or to the "approx".
The other thing I'm confused about is that I thought desalination was upstream of cesium removal in the Fuku-ichi water treatment sequence, so I don't see why cesium levels should be low.
  • #11,831
Seems clear enough from Tsutsuji-san's postings:
http://mainichi.jp/select/jiken/news...40092000c.html Beta radiations due to strontium and other substances are between 100,000 Bq/cm³ and 1,000,000 Bq/cm³. The strontium concentration in the leaked water is about one million times as high as the standard set by the nuclear power regulating law for sea releases.The building's area is 30 m x 30 m. As the leaked water's height was about 5 cm, the leak's volume is 30 x 30 x 0.05 = 45 m³.
http://www.nytimes.com/2011/12/05/wo...ear-plant.html
The thing that throws a US reader is the reference to a 'puddle' of contaminated water, which does not convey the same impression as learning of a 45 ton or even 200 ton leakage.
In fairness to TEPCO, they have thus far treated some 180,000 tons of water, so perhaps by that standard, the term 'puddle' is quite appropriate.
  • #11,832
etudiant; absolutely clear on the volume now. I don't know how I missed it.
  • #11,833
5.8 trillion becquerels ! As far as leaks go ,how would this score on the INES scale ?
Is there much point in TEPCO just reducing cesium contamination and leaving other isotopes undiminished? Did that official really drink all that strontium?
  • #11,834
As far as I understand, the leak is in the last stage of the process, where the salty waste liquid produced in the reverse osmosis is further concentrated by evaporation. And apparently it is from the more concentrated side of that process as well. Certainly not from the water that's being recycled into the reactors.
As to why they are leaving it as liquid, I'm no chemist but assume that it might have something to do with the high salt content messing up the possibilities to extract strontium from the liquid, and it is therefore for time being stored as it is.
The amount of leak appears to be somewhat unclear: I got the impression that the 45 tons would be the amount found inside the building - I don't now how that relates to the amount that has actually leaked outside or found its way to the sea.
  • #11,835
http://www3.nhk.or.jp/news/html/20111205/t10014421611000.html Concerning strontium, the analysis takes about two weeks. The NISA requests Tepco to write a report on the cause of the leak and on countermeasures. The water leaked for 21 hours or less before Tepco found it. A concrete barrier recently installed to contain leaks, had cracks.
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111205_01-e.pdf Status of the water leakage
http://mainichi.jp/select/biz/news/20111206k0000m040083000c.html According to Tepco, 300 l flowed outside the building.
  • #11,836
You are probably thinking about Yasuhiro Sonoda, parliamentary secretary at the cabinet office who drank water in front of journalists about 5 weeks ago.
That water was not from the basements of the wrecked units 1-3, where the water in this current leak originates from. It was from units 5 and 6, whose fuel rods are still intact, as one air-cooled diesel in unit 6 survived the tsunami to provide power for the cooling.
  • #11,837
I just noticed that the recent core melt analysis stuff is available in english:http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_04-e.pdf
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_05-e.pdf
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_06-e.pdf
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_07-e.pdf
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_08-e.pdf
Not had time to read it all yet but as per my earlier post based on the Japanese version, we see a repeat of stuff first mentioned a long time ago but not dwelled upon that much, such as a presumption that there was a drywell leak 22 hours after the earthquake at reactor 2. And somewhere they also mention one of the subjects that interests me, why the reactor 2 suppression chamber water temperature readings went up in the latter part of October - they say its because after water injection rate was increased, steam decreased so there was more hot water ending up in the suppression chamber. Speaking of which, I see that s/c temperatures at 2 have started creeping up again in recent days after falling for quite some time.
  • #11,838
I don't understand one thing, from those analysis we can see that tepco think that part of unit 2 core is still undamaged, but I see problem here, they also recalibrated water level sensor and from data we can see that it is -5m from top of 4m fuel rods. So it is possible that fuel will not melt without cooling ?
  • #11,839
Good point, it's possible that if that level is accurate and there is still standing material then the rising steam is sufficient to provide a modicum of cooling.
That is dependent on their hypothesis being correct, of course.
  • #11,840
SteveElbows said:
These are the press conference / workshop slides. The the main report ( http://www.tepco.co.jp/nu/fukushima-np/images/handouts_111130_09-j.pdf ) (207 pages) is still not available in English.
"All fuel melted through PCV from original position" on page 20 of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_04-e.pdf is presumably a translation mistake. The Japanese text at http://www.tepco.co.jp/nu/fukushima-np/images/handouts_111130_07-j.pdf says "all fuel moved downwards from original position". Then, "Further, as there is a high probability that RPV damage occurred, we estimate that a considerable amount dripped down to PCV bottom".
  • #11,841
I don't see where they say that?
Given current water levels and the fact that they estimate that less than 3% of fuel is uncovered, it would seem that all the fuel has relocated to the bottoms of the RPVs in units 2&3 and even further to the bottom of the PCV in the case of Unit 1.
  • #11,842
Well, in http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_04-e.pdf they state that
Even though the fuel was damaged and melted , a part of the fuel remains inside the core of RPV and the others dropped to the bottom of RPV plenum or the PCV pedestal.
I think the 'uncovered' is just a translation error and they mean 'uncooled'.
  • #11,843
See the green colour squares labelled "Damaged fuel piled (Maintain of fuel rod figure)" on page 8 (9/29) of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_08-e.pdf
I agree. The "3% (or less) uncovered" result and the "Unit 2 result of estimation with analysis code" ( page 8 (9/29) of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_08-e.pdf ) seem to contradict each other.
"Therefore, it is evaluated that all the moved fuel is expected to be cooled directly by water injection." written on page 23 (24/28) of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_04-e.pdf could alternatively be translated as "Therefore, it is evaluated that all the moved fuel is being cooled in a condition where it is largely in contact with water". It sounds like that the question of how the unmoved fuel is being cooled is left unanswered.
Well, after reading http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_06-e.pdf it seems that they mean just the opposite, because they say :
Considering the results that water injection from the core spray system exerted a great effect (...) In the new model, a part of the injected water directly removes the heat from the uncovered core.
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_06-e.pdf page 2 (3/10)
It sounds like that what they mean by "uncovered" means "uncovered and cooled by core spray system or cooled by heat conduction/convection/radiation".
  • #11,844
  • #11,845
zapperzero said:
Yeah, they're saying it should look a bit like TMI on the inside, which does not seem to be consistent with their other estimates.
Even their "Conservative scenario Approx.109 hours after the earthquake" on page 8 (9/29) of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_08-e.pdf has 12 little orange squares above original bottom of fuel. That makes 12% and this is still higher than the 3% result from the "improved JAEA heat model" explained on http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_06-e.pdf
The other scenario translated as "Based on the indicator" on the English version can alternatively be translated as "relying on indicated values".
  • #11,846
Yeah, thanks. You are right.
3%... I thought it'll be more than that: the change when they switched on the CSS was really impressive.
Of course the cooling of the covered fuel was also improved by the water amount pushed in through the CSS, so it's logical... But a bit sad.
  • #11,847
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111206/index.html According to Tepco, about 150 litres of water contaminated with beta-radiating substances such as strontium flowed to the sea. A maximum of 300 litres flowed through the cracks in the building's foundation. The 150 litre figure is the result of an estimate based on data such as leaking time.
The density of radioactive materials contained in the water leaked is 2.6 x 10^10 Becquerel (provisional) in total, calculating from
the density of strontium 89, 90, cesium 134, and 137.
Strontium 89: 7.4 x 10^4 Bq/cm3 (1.1 x 10^10 Bq)
Strontium 90: 1.0 x 10^5 Bq/cm3 (1.5 x 10^10 Bq)
Cesium 134: 1.6 x 10^1 Bq/cm3 (2.4 x 10^6 Bq)
Cesium 137: 2.9 x 10^1 Bq/cm3 (4.4 x 10^6 Bq)
(Water collected on Dec 4, 2011. Amount of strontium estimated from the density of all-beta radioactive materials.)
This value accounts for 12 % of 2.22 x 10^11 Bq, which is the annual discharge control target of radioactive liquid waste at
Fukushima Daiichi Nuclear Power Station.
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/111206e16.pdf
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111206/1910_reikyaku.html Suspecting that it caused a delay in the response to the accident, the NISA investigated and heard witnesses in August on the question whether plant managers had mistakenly believed unit 1's isolation condenser was running while it was not. The results of the NISA's investigation were publicly released on 6 December : the managers were not aware that a plant operator had closed the IC's valve, and it is 8 hours after the earthquake, after 11 PM, after knowing that the radiation inside reactor building was rising, that they first grasped the IC status. It is possible that this caused a delay in the response to the accident.
The documents released by the NISA:
http://www.meti.go.jp/press/2011/12/20111206002/20111206002-2.pdf List of questions (asked by the NISA to the witnesses)
http://www.meti.go.jp/press/2011/12/20111206002/20111206002-3.pdf The NISA's conclusions
(they cover a wide range of topics, not only unit 1, not only unit 1's IC)
  • #11,848
It seems they don't take into account the additional heat from the steam-zirconium exothermic reaction.There suppose to be hydrogen at unit 3 at least, so some part of zirconium reacted. How much?
  • #11,849
Cheers Joe , I'm convinced you are spot on dead accurate. :smile:
Question is ,what impression "TEPCO" :biggrin:are trying to convey to the general public.;)
  • #11,850
Oops I made a mistake. The documents were talking about the temperature rise of reactor 1 suppression chamber in the past, not reactor 2. I think they mentioned reactor 3 s/c temp as well.
The interesting temperatures mentioned for reactor 2 are the ones for the CRD housing, and SRV, some of which are much higher than the other temperatures we are used to seeing regular data about. (page 6 of http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111130_05-e.pdf )
49K
448K
273K
16K
11K