Low load factors in distribution transformers lead to increased system losses and voltage drops due to higher reactive currents, which cause voltage drops to subtract directly from the system. This occurs because the series impedance is primarily inductive, resulting in reactive currents contributing to voltage drops differently than real currents. When currents are high for shorter periods, as seen with low load factors, the power loss in the line increases significantly compared to a steady load. The discussion also highlights confusion between load factor and power factor, emphasizing that a low load factor indicates a more variable load, which is less efficient. Understanding these concepts is crucial for managing energy distribution effectively.
rozan977
Messages
9
Reaction score
0
My lecturer, in the notes he provided to us mentioned that low load factor of a distribution transformer results in higher system losses and voltage drops. I thought the by higher system losses he means the iron losses in transformer which is comparably higher in no-load and lower load conditions. But I just couldn't figure out how low load factor causes voltage drops in system?
 
Engineering news on Phys.org
He's probably referring to the effect of reactive current causing comparatively much more voltage drop in upstream reactive impedance.

Because the series impedance of the power system is primarily inductive, then the voltage drops due to reactive current tends to subtract directly, whereas those from real current components add vectorally at right angles.

For example, say you had a load taking 1.0 pu reactive current and the series impedance was j0.1 pu. The required generator voltage is 1.1 pu (the voltage drop is in phase so adds algebraically). Now consider the same case but with 1.0 pu real current being supplied. The required generator voltage is now only 1.005 pu (volt drop adds at 90 degrees).
 
uart, I think you are confusing 'Load factor' with 'power factor'.
@rozan977, I think the lecturer is trying to explain what would happen in a distribution system already in existence if the Load factor goes low. In such case, assuming same average monthly consumption, a low load factor means, high currents for shorter period of time, (as compared to the currents being distributed in time, in case of higher load factor).
Higher currents obviously results in higher voltage drop (during the high current period). If we do the maths, we can also see that, when currents are higher for short period and less for longer period (instead of evenly spreading out), the power loss in the line will be higher.
for example, For a building, the current is 10A for whole 24 hours (load factor of 1)
Then its daily energy Loss = 10^2*R*24
In another building, the current is 20A for 12hrs and 0A for 12hrs (same average daily energy). This gives load factor of 0.5.
Then its daily energy loss = 20^2*R*12, which is double of the previous case.
 
I_am_learning said:
uart, I think you are confusing 'Load factor' with 'power factor'.

I think the lecturer is trying to explain what would happen in a distribution system already in existence if the Load factor goes low. In such case, assuming same average monthly consumption, a low load factor means, high currents for shorter period of time, (as compared to the currents being distributed in time, in case of higher load factor).

No, actually I think you're confusing load factor with something like duty factor or duty cycle (the ratio of average to peak).

The load factor of a transformer (at any given point in time) is simply the operating power (at that time) as a ratio or percentage of it's rated power. Since the magnetizing reactance draws approximately constant reactive current (independent of load) then a low load factor implies a worse power factor. So no, I'm not confusing them, they are in fact related.
 
Last edited:
In the book "ELECTRIC POWER DISTRIBUTION
EQUIPMENT AND SYSTEMS", Author T.A. Short says
T.A. Short said:
• Load factor — The ratio of the average load over the peak load. Peak
load is normally the maximum demand but may be the instantaneous
peak. The load factor is between zero and one. A load factor
close to 1.0 indicates that the load runs almost constantly. A low load
factor indicates a more widely varying load. From the utility point
of view, it is better to have high load-factor loads. Load factor is
normally found from the total energy used (kilowatt-hours) as:
LF = kWh/(dkW*h)
where
LF = load factor
kWh = energy use in kilowatt-hours
dkW = peak demand in kilowatts
h = number of hours during the time period
 
The definition I've got here is:

Transformer Load Factor : Current load / rated load.

Edit. Just googled a few papers on the subject and some authors are using the definition of "current power/rated power" while others are using "average/peak". So yeah, take your pick. :cry:I guess the op will have to let use know what particular definition of "load factor" he's using.
 
Last edited:
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top