After replacing the bearings in a 24V, 15A DC motor, speed control issues have arisen, with the motor running but lacking speed regulation. Potential problems include damage to the stator and rotor windings, or issues with the tacho-generator or encoder due to a misaligned shaft. It's suggested to check the mechanical connections and ensure that the encoder is functioning properly using an oscilloscope. Additionally, verifying the commutator coils and brushes can help identify any failures affecting motor stability. Troubleshooting these components is essential for restoring proper motor function.
Arifur
Messages
8
Reaction score
0
After bearing failure of 24V, 15A dc motor. We change the bearing of the dc motor. But after changing it the motor is running forward/ reverse but there is no control over the speed.

Where is the problem? Is that in the techo or drive card?
Any body please help.

Helping in highly appreciated...
 
Engineering news on Phys.org
Suggestions:

1) The stator and rotor have scratched each other, and some of the windings have been damaged.

2) The tacho-generator or encoder has been damaged, due to a skew shaft.
 
Thnx Hesch for your suggestion, but there is no screech between rotor and stator.
In case of winding failure it won't run, isn't it?
 
Arifur said:
In case of winding failure it won't run, isn't it?
I don't know how your motor is made up, but I think that electronic commutation of the motor is used. In this case I'm sure that the drive will report an error in a coil.

In case of a mechanical commutation, there is a lot of coils in the motor, and if one of these are damaged, the motor will be unstable. The drive, which then is a simple dc-drive, will not detect/report an error.

But what about the tacho-generator/encoder? Connect an oscilloscop and see if they are running stable.

( I've seen so many times in case of an error, that the mechanical connection from motor shaft to e.g. encoder shaft is not correctly fastened. )
 
Here is a good troubleshooting guide that may be of some help.

To expand on what Hesch is saying about multiple commutator coils: when you check the brushes, if there are more than one pair, you can remove some of them so there is only one pair left, (that is two brushes on directly opposite sides). Now when you rotate the armature and read the ohmmeter you can check each of the commutator windings separately, as you slowly turn the rotor by hand (with all power disconnected!) Be sure to replace all the other brushes when done. Don’t forget to check the tachometer (if equipped) for output signal.
 
  • Like
Likes Hesch
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...