Phase to phase wiring question
In summary, the conversation is discussing the use of single phase and three phase power in a machine and how the two phases create a potential difference without using a neutral wire. The conversation also touches on the concept of corner-grounded delta connections and how they work in relation to three phase systems.
raider94
I am servicing a machine that uses a 3 phase power supply. Some of the components (motor, compressor, fan) use 3 phase power. Other components (solenoids) use single phase (phase to phase) tapped from L1 and L3. I understand regular single phase-120v and a nuetral. The nuetral creates the potential for the current to flow. How does the two hots, in this case (L1 and L3) create a potential without using a nuetral wire? If a soleniod is using two hots out of phase, how is that single phase and how does the current flow? How is there a potential created between the two phases?
Thanks for any help.
You derive a neutral by having a transformer with a 'star' (wye) secondary.
http://ecmweb.com/mag/electric_understanding_basics_wye/
The voltage between phases is sq rt 3 times the phase to neutral because the phases are 120 deg out with one another and the resulant sine is the vector sum.
So the phase to phase voltage is 208 Volts.
I know all that but how do you get current to flow between two phases? What is the potential?
There is a potential difference since they are out of phase. Take a look here for a graphic example.
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/hsehld.html
In this household type of circuit (i.e. 180 electrical degrees out of phase), when one leg is at a positive peak potential, the other leg is at a negative peak potential. Hence the peak-to-peak voltage is the vector sum of the two. Since both are connected in the same circuit current flows.
If you are only using two legs of a three-phase system, the voltage (and current) will be 120 electrical degrees out of phase as stated above.
CS
Thanks, that clears it up a bit. But how do you get 240 from that? I can see how L1 is finding its potential when L2 goes negative. when the top of the wave at L1 is at peak value, is that 120? if so, how can the total voltage be 240? If the bottom of the wave at L2 is only a potential, it would seem to me that your only getting 120 because the bottom half cancles out the other 120
. Thanks again for your help.
If L1 is at 120, then L2 is at -120. 120 - (-120) = 240
Ok that makes sense. Now what about this:
When I measure L1 to ground I get 220 voltage when I measure L2 to ground I get 0 and when I measure L3 to ground I get 200. How can L2 to ground be 0 if its 3 phases? I am in Japan by the way. Thanks for any help.
Sounds like you dropped a phase. The other two should be better balanced, too. Can you check at the panel to make sure you aren't missing something?
No. The japanese verified it as well. L2 is a nuetral, grounded at the transformer in a delta configuration. I don't understand it, how L2 can be nuetral in a 3 phase system. Also,if I dropped a phase, the 3 phase motor and compressor would be single phasing and making troubles.
Sounds like you have a corner-grounded delta connection. This will not affect the way a three-phase system works. The three phases are still 120 electrical degrees apart. Hence, you have 0 volts between ground and ground (i.e. ground and L2) and your equipment still works. Check the phase-to-phase voltage to confirm.
Hope this helps.
CS
Sounds like Ground is being tapped off of L2.
L2 is not at 0 electrical potential... The dilema here is that you are mesuring the difference between the same leg...think about it...L2 is zero in regards to what?...("Itself")
In other words you are just measuring L2/GRND in contrast to L2/GRND.
Corner-grounded delta connection configurations are typically for "ungrounded" systems...
Thats why sparks arn't flying.
So L2 is a normal phase...its just being used as a ground or "return" path to compensate your ungrounded 3 phase system.
Hope this helps.
That's how corner-grounded delta connections work. The corner is grounded at one leg.
L2 is at 0 electrical potential when he references it to ground (see post #7 above). In a corner-grounded delta connection 0 volts would be read at the corner ground with respect to ground since it is grounded. In other words there is no potential difference between a leg that is grounded and ground (actually there is a very very small difference but it is normally neglected).
Corner-grounded delta connections can be used for both ungrounded an grounded systems. Since transformers electrically decouple a circuit, grounds from the rest of the system are not passed along. There just can't be two grounds in the transformer (i.e. no center tap ground for lighting circuits in addition to the corner ground - only one or the other).
Grounds are not used as return paths for various reasons.
CS
Please explain what I convoluted.
I will send you a personal message (PM) about why your post was deleted. It violated PF forum guidelines. You have already received a PM from the initial deletion.
1. What is phase to phase wiring?
Phase to phase wiring is a type of electrical wiring where the power is transmitted from one phase conductor to another phase conductor. This type of wiring is commonly used in three-phase power systems.
2. How does phase to phase wiring differ from single phase wiring?
Phase to phase wiring involves three conductors, while single phase wiring only involves two conductors. Additionally, phase to phase wiring is used for heavier loads, while single phase wiring is used for smaller loads.
3. What are the benefits of using phase to phase wiring?
Phase to phase wiring allows for a more efficient distribution of power, as it can handle larger loads and reduce voltage drop. It also allows for the use of three-phase motors, which are more powerful and efficient than single phase motors.
4. Is phase to phase wiring safe?
Yes, phase to phase wiring is safe when installed and used correctly. It is important to follow proper wiring procedures and use appropriate protective devices to ensure safety.
5. Can phase to phase wiring be used for residential homes?
Phase to phase wiring is typically used in commercial and industrial settings, but it can also be used in larger residential homes with high power demands. However, it may not be necessary or cost-effective for smaller residential homes.
  • Electrical Engineering
14K