Standard Form for second order systems.

Click For Summary
SUMMARY

The discussion focuses on the standard form of second-order systems, specifically the transfer function represented as T(s) = (ks + c) / (s² + as + b). The standard form is defined as ωn² / (s² + 2ζωn s + ωn²), where ωn is the natural frequency and ζ is the damping ratio. The participants emphasize that the numerator's constant does not influence the damping ratio or overshoot parameters, as these are determined by the system's ratios. Understanding how to manipulate these parameters allows for achieving desired performance metrics such as rise time, maximum overshoot, and settling time.

PREREQUISITES
  • Understanding of second-order system dynamics
  • Familiarity with transfer functions and their representations
  • Knowledge of natural frequency (ωn) and damping ratio (ζ)
  • Experience with control system performance metrics (rise time, overshoot, settling time)
NEXT STEPS
  • Study the derivation of the standard form for second-order systems
  • Learn how to calculate rise time and settling time from transfer functions
  • Explore the effects of varying the damping ratio on system performance
  • Investigate the role of low-frequency gain in control systems
USEFUL FOR

Control engineers, system designers, and students studying control theory who are looking to optimize second-order system performance and understand the implications of parameter adjustments on system behavior.

zoom1
Messages
63
Reaction score
0
Suppose there's a system with given uncertain parameters. And I would like to obtain certain Rise time, max. over shoot, settling time by adjusting those parameters.

Let's say this is the second order system;

T(s) = (ks + c) / (s2 + as + b)

First of all; for a second order system there is a standard form which is;

Wn2 / s2 + 2ζωns + ωn2

As we have to have the Wn2 in the numerator, it's not that way always. Just like in the example. So, what am I suppose to do at that point ?

If the transfer function T(s) looks like exactly the standard form, I could get the desired values by changing parameters. I think.
 
Engineering news on Phys.org
zoom1 said:
First of all; for a second order system there is a standard form which is;

Wn2 / s2 + 2ζωns + ωn2
Parentheses, please!

ωn2 / ( s2 + 2ζωns + ωn2 )

The constant in the numerator doesn't affect ζ, nor ωn, nor parameters such as % overshoot, rate of gain fall-off, etc., since these are calculated as ratios. The numerator is just a scaling factor for the plots.

The general expression is: A.ωn2 / ( s2 + 2ζωns + ωn2 )

where A can be seen to be the low frequency gain of this system.
 

Similar threads

Replies
1
Views
4K
Replies
9
Views
3K
Replies
3
Views
7K
  • · Replies 2 ·
Replies
2
Views
4K
Replies
1
Views
3K
Replies
14
Views
3K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K