Thevenin Generator: Maximum Active Power & Calculation

Click For Summary

Discussion Overview

The discussion revolves around the calculation of the Thevenin equivalent circuit, specifically focusing on the maximum active power transfer and the calculation of the open circuit voltage (Uab)0. Participants explore various methods for determining voltages and currents in a circuit using node potential analysis, while also addressing concerns about the behavior of voltage generators and current flow in circuits.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant calculates Zab as 3-3j and expresses confusion about calculating (Uab)0, proposing a formula that includes currents not shown in the circuit diagram.
  • Another participant asserts that current flow must return to its source, emphasizing that a voltage generator does not require current to be flowing through it.
  • Concerns are raised about the inclusion of the generator in calculations, with participants debating how voltage is defined in the absence of current flow.
  • One participant mentions that in calculating open circuit voltage, the impedance in question should be removed while retaining all voltage and current sources.
  • There are discussions about ideal voltage and current sources, including potential contradictions that could arise in circuit analysis.
  • Another participant questions the numerical value of Zab given the lack of numerical values for certain components, suggesting a need for a clearer derivation of equations used in nodal analysis.
  • One participant expresses frustration over not understanding their mistakes after several hours of work, seeking clarification on their approach.
  • Corrections are suggested to the equations presented, with one participant indicating they have resolved their issues after further analysis.
  • A new problem is introduced regarding the calculation of complex power for a capacitor, with a participant expressing confusion over their results.

Areas of Agreement / Disagreement

Participants express differing views on the role of voltage generators in circuit analysis and the correct application of nodal analysis. There is no consensus on the correct approach to calculating (Uab)0 or the complex power of the capacitor, indicating ongoing debate and uncertainty.

Contextual Notes

Participants mention missing assumptions and the need for numerical values in their calculations, which may affect the validity of their approaches. There is also a lack of clarity regarding the definitions and roles of certain voltages and currents in the circuit.

Who May Find This Useful

This discussion may be useful for students and practitioners in electrical engineering or physics who are grappling with circuit analysis, particularly in the context of Thevenin equivalents and power calculations.

Edy56
Messages
38
Reaction score
5
Homework Statement
In the electrical circuit shown determine:
Impedance Z so that it develops on it maximum active power and calculate that power.
Relevant Equations
none
komp.png

So I have calculated Zab which is 3-3j (it's correct).
Now I have to calculate (Uab)0. This is where I just get completely lost.
In my opinion:
(Uab)0=E3+I3*R3+Ic1*Xc1+E4

Note: I recognize these currents are not shown in the picture, but based on their indexes and basic logic I hope you understand where I imagine them being.

Now obviously I am missing I3 and Ic1 so I decided to try to use node potential method to determine their values.
These are my equations:

U10*(1/(jXl1+R1)+1/(-jXc)+1/R3)-U20*(1/jXl1) = E1/(jXl1+R1) +E3/R3

U20(1/(R1+jXl1)+1/(-jXc2))-U30(1/-jXc2)-U10(1/(jXl1+R1+)= J+ E1/(jXl1+R1) + E2/(-jXc2)

My biggest concern is regarding the branch with R3and E3. Because of the break at node 'a', I would assume there is no current flowing there, but I have a generator there so I am confused.
 
Physics news on Phys.org
Edy56 said:
My biggest concern is regarding the branch with R3and E3. Because of the break at node 'a', I would assume there is no current flowing there, but I have a generator there so I am confused.
Current flow always has to return in the circuit to where it started, where you measure it leaving from. This is from conservation of charge, you can't just generate electrons, you can only move them. E3 is a voltage generator, it doesn't necessarily have to have current flowing through it.
 
DaveE said:
Current flow always has to return in the circuit to where it started, where you measure it leaving from. This is from conservation of charge, you can't just generate electrons, you can only move them. E3 is a voltage generator, it doesn't necessarily have to have current flowing through it.
I have seen that in similar cases when calculating (Uab)0 they also add the generator. But that doesn't make really sense to me. There is no current flowing through it, and I get that te generator doesn't necessarily need it, but where does the voltage come from? Voltage is current * resistance.
 
Edy56 said:
I have seen that in similar cases when calculating (Uab)0 they also add the generator. But that doesn't make really sense to me. There is no current flowing through it, and I get that te generator doesn't necessarily need it, but where does the voltage come from? Voltage is current * resistance.
When they calculate the open circuit voltage they remove the impedance in question, Z, in your case. All voltage and current sources are still included with their values. Then you calculate the voltage across the terminals where Z used to be.

E3 makes the voltage defined, whether there is any current or not. It is an ideal voltage source and makes whatever current it needs to to make it's defined voltage. Same for current sources, but they make whatever voltage is required.

There are exceptions that you should never see in a well posed problem. That is a generator that can't make the voltage (or current) it needs to, usually because the current (or voltage) require would be infinite. Or that make contradictions, like requiring a voltage to be two different values. Some examples of this are:
1) An ideal voltage source with a short circuit, a 0Ω load. This would require infinite current.
2) An ideal current source with an open circuit, an ∞Ω load. This would require infinite voltage.
3) Two ideal voltage sources connected in parallel with different values. Actually, this is really any circuit loop that only has voltage sources in it. They would then all have to sum to zero around the loop. This is KVL.
4) Two ideal current sources connected in series with different values. Actually, this is really any circuit node that only has current sources connected to it. They would then all have to sum to zero at that node. This is KCL.
 
DaveE said:
When they calculate the open circuit voltage they remove the impedance in question, Z, in your case. All voltage and current sources are still included with their values. Then you calculate the voltage across the terminals where Z used to be.

E3 makes the voltage defined, whether there is any current or not. It is an ideal voltage source and makes whatever current it needs to to make it's defined voltage. Same for current sources, but they make whatever voltage is required.

There are exceptions that you should never see in a well posed problem. That is a generator that can't make the voltage (or current) it needs to, usually because the current (or voltage) require would be infinite. Or that make contradictions, like requiring a voltage to be two different values. Some examples of this are:
1) An ideal voltage source with a short circuit, a 0Ω load. This would require infinite current.
2) An ideal current source with an open circuit, an ∞Ω load. This would require infinite voltage.
3) Two ideal voltage sources connected in parallel with different values. Actually, this is really any circuit loop that only has voltage sources in it. They would then all have to sum to zero around the loop. This is KVL.
4) Two ideal current sources connected in series with different values. Actually, this is really any circuit node that only has current sources connected to it. They would then all have to sum to zero at that node. This is KCL.
U10*(1/(jXl1+R1)+1/(-jXc))-U20*(1/jXl1) = -E1/(jXl1+R1)

U20(1/(R1+jXl1)+1/(-jXc2))-U30(1/-jXc2)-U10(1/(jXl1+R1)= J+ E1/(jXl1+R1) + E2/(-jXc2)

are these correct then? I removed E3 and R3
 
Edy56 said:
U10*(1/(jXl1+R1)+1/(-jXc))-U20*(1/jXl1) = -E1/(jXl1+R1)

U20(1/(R1+jXl1)+1/(-jXc2))-U30(1/-jXc2)-U10(1/(jXl1+R1)= J+ E1/(jXl1+R1) + E2/(-jXc2)

are these correct then? I removed E3 and R3
No. I don't see any method to your process, like you're guessing. That won't work.
 
DaveE said:
No. I don't see any method to your process, like you're guessing. That won't work.
I am not guessing. I am using the node potential method.
 
Edy56 said:
I am not guessing. I am using the node potential method.
I might be making a mistake somewhere, but I do not see it nor do I understand it. So if you could tell me where I am wrong so I can try to see why I would be thankful because I had been at this problem for 5 hours now and I really do not see where I am making mistakes.
 
How were you able to calculate a numerical value for Zab when XC1, XC2, and XL1 have no numerical values?

What nodes are the voltages U10 and U20? If those are the voltages at nodes 1 and 2 why would you call those voltages U10 and U20 rather than U1 and U2?

Rather than just presenting final equations, show how you derived them starting with the fundamental steps of a nodal analysis. That way, we could see where you made a mistake.
 
  • #10
The Electrician said:
How were you able to calculate a numerical value for Zab when XC1, XC2, and XL1 have no numerical values?

What nodes are the voltages U10 and U20? If those are the voltages at nodes 1 and 2 why would you call those voltages U10 and U20 rather than U1 and U2?

Rather than just presenting final equations, show how you derived them starting with the fundamental steps of a nodal analysis. That way, we could see where you made a mistake.
okay so I do have numerical values, I did not show them because I am just interested in just knowing how to solve for (Uab)0.

As for the nodes, I don't know what to tell you. That's just how we are told to solve problems. Here is the "formula":

nodes.png
 
  • #11
Edy56 said:
U10*(1/(jXl1+R1)+1/(-jXc))-U20*(1/jXl1) = -E1/(jXl1+R1)

U20(1/(R1+jXl1)+1/(-jXc2))-U30(1/-jXc2)-U10(1/(jXl1+R1)= J+ E1/(jXl1+R1) + E2/(-jXc2)

are these correct then? I removed E3 and R3
U10*(1/(jXl1+R1)+1/(-jXc1))-U20*(1/(R1+jXl1)) = -E1/(jXl1+R1)

I've shown in red corrections to two mistakes I see.
 
  • #12
solved it now, thank you
 
  • #13
The Electrician said:
U10*(1/(jXl1+R1)+1/(-jXc1))-U20*(1/(R1+jXl1)) = -E1/(jXl1+R1)

I've shown in red corrections to two mistakes I see.
Okay i have another problem. I have to determine complex power of the Xc1.
I have calculated that U10=5 (this Is correct)
I know that Xc1=5
So logically I=U10/-jXc1=j
Sc=1/2*-jXc1*|I|^2
Sc=1/2*-j5
Sc=1/2*-j5 - this Is not correct, whyy I am supposed to get 25*(-j)/2
 

Similar threads

  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 26 ·
Replies
26
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
2
Views
2K
  • · Replies 21 ·
Replies
21
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K