What Is the Apparent Power in a Circuit with a Power Factor of 0.72?
In a circuit with a power factor of 0.72 and a true power dissipation of 375W, the apparent power can be calculated using the formula S = P / PF, resulting in an apparent power of approximately 520.83 VA. The relationship between voltage, current, and impedance is also discussed, with the current determined to be 12 Amps based on a 120V supply and a 10Ω resistance. The discussion emphasizes the importance of understanding complex power and its components, including real and reactive power. The calculations confirm that the apparent power is correctly derived from the true power and power factor. Understanding these concepts is crucial for analyzing circuit behavior and impedance.
Angusbrooks
A circuit has a power factor 0.72 lagging and the power dissipated is 375w.
Determine:
(A) Apparent power
Relevant equations:
ohms law V = I x R
apparent power (S) = supply voltage (Vs) x Current (I)
Attempt:
Current =
Voltage
Resistance
120v
10Ω
= 12Amps
∴ Apparent power (S) = Supply voltage (Vs) x Current (I)
120V x 12 Amps
= 1440 VA
I have seen another equation where it states that true power is the power dissipated at 375W therefore my second attempt which I am very unsure of as I cannot locate the stated equation within my book:
altenative attempt
S (Apparent power) =
P (True power)
PF (power factor)
375W
0.72
= 520.83333
please help?
Angusbrooks said:
Current =
Voltage
Resistance
120v
10Ω
= 12Amps
The current is V/(Z+R) where Z is an unknown impedance.
altenative attempt
P (True power)
PF (power factor)
375W
0.72
= 520.83333
This is right. I take it the question is asking for the unknown impedance Z?
I think maybe a little review of what S is will help. Suppose a sinusoidal voltage V is applied to an impedance Z. Then a current I will flow that is also sinusoidal but at some phase offset. In the time domain the voltage is Vcos(wt) and the current is Icos(wt-θ) where θ could lead or lag depending on the load.
The instantaneous power is
P(t) = VI cos(wt)cos(wt-θ) = VI [cos2(wt)cos(θ) + sin(wt)cos(wt)sin(θ)]
The average power over a period is
Pav = (VI/T) ∫[cos2(wt)cos(θ) + sin(wt)cos(wt)sin(θ)]dt
= (VI)(w/(2∏)) ∫(1+cos(2wt))cos(θ)/2 dt
= (VI)(w/2∏)cos(θ)(1/2)(2∏/w)
= (VI/2)cos(θ)
= VrmsIrmscos(θ)
The complex power S is defined as
S = VI*
where * is complex conjugate and both V and I are rms voltages.
The complex conjugate on I is taken so that the angle of S will be the difference in phase between V and I, which is what is important in the average power calculation above. If you sketch S on the complex plane, its magnitude will be |VrmsIrms| and its angle will be θ, the angle between the V and I phasors. If you take the real part of S,
Re(S) = |S|cos(θ) = VrmsIrmscos(θ)
This is the average power consumed by the load. So S projected on the real axis in the complex plane is the real power. S projected on the imaginary axis is indicative of the power being stored and released in the reactive components (this can be seen from the instant power equation above); no average power is consumed by reactive components. Over a period, energy is consumed by the reactive components and then the same amount is released; this extra current must be absorbed and supplied by the source through the cycle.
In your problem you are given the real power of 375W. This is S projected on the real axis. So the magnitude of S is 375/cos(θ) = 520.8VA as you found.
Since you now know |S|=|VrmsIrms| and you know Vrms, you also know |Irms|. Given V, |I| and information on the angle between V and I, you should be able to determine the total impedance seen by the source.