In summary, 400 kV power lines typically have 6 pairs of wires, 3 on each side, to provide redundancy and higher power carrying capacity. The phases are transmitted in pairs, with spacers to prevent them from touching. This also reduces corona losses and audible noise. The pairing of the wires also allows for easier load control and potential for switching between circuits in case of failure. Bundle conductors are also used to increase current carrying capacity and reduce reactance.
  • #1
RedX
970
3
Why do 400 kv power lines have 6 pairs of wires, 3 on each side? Shouldn't there only need to be 4 wires, a ground/neutral wire and 3 wires for 3 phases?
 
Engineering news on Phys.org
  • #2
The ground wire comes after the distribution transformer only...
 
  • #3
Three phase doesn't need a ground/neutral for power transmission Hence they will come in multiples of 3. Sometimes one or two ground lines are used as lightning protection where there are long spans.

There are various configurations, from three wires up depending on needs. Multiple circuits give both redundancy and higher power carrying capacity.

I would speculate that they may also be configured to reduce the small but nonzero radiative losses.
 
  • #4
Here's a link to a picture of a 400 kV pole:

http://www.emfs.info/Sources+of+EMFs/Overhead+power+lines/Parts+of+a+power+line.htm

jambaugh said:
Three phase doesn't need a ground/neutral for power transmission Hence they will come in multiples of 3. Sometimes one or two ground lines are used as lightning protection where there are long spans.

There are various configurations, from three wires up depending on needs. Multiple circuits give both redundancy and higher power carrying capacity.

I would speculate that they may also be configured to reduce the small but nonzero radiative losses.

Call the 3 phases A, B, and C. Are the phases transmitted in pairs, AB, BC, and AC? Because in the pictures of the power lines I've seen, they are sent in pairs with spacers preventing them from touching. But why pair them at all? Why not just have 3 wires of A, B, and C?

Redundancy makes sense, but I'm not sure about power carrying capacity. If more power is needed, then the turbines in the generator just push harder, and more power goes down through the line. I'm not sure why you need multiple lines for that.

Also if you have twice as many lines don't you get twice the losses?
 
  • #5
RedX said:
Redundancy makes sense, but I'm not sure about power carrying capacity. If more power is needed, then the turbines in the generator just push harder, and more power goes down through the line. I'm not sure why you need multiple lines for that.

Also if you have twice as many lines don't you get twice the losses?
No. The two pairs would share the load, and each would have less current. That equals less resistive loss.
 
  • #6
The picture is very clear. There are two circuits; one on the left side of the tower and one on the right side of the tower. The spacers between two conductors, say on the left side, is to prevent them from wind damage and are the same phase & potential.
 
  • #7
RedX said:
Here's a link to a picture of a 400 kV pole:

http://www.emfs.info/Sources+of+EMFs/Overhead+power+lines/Parts+of+a+power+line.htm
The direct link doesn't work but I cut and pasted the link and did find the pic.
Note that the spacers between the pairs are not insulators, they are just spacers to keep the wires a fixed distance apart (probably for mechanical reasons.) Note that the spacing is small so even if the spacers are insulating there can't be much potential difference between the pairs. Consider what would happen if a buzzard landed on one of the pairs. Even a moderate 100V would fry it.

I imagine the pairing with spacers is to keep the cables from swinging in the wind as well as additional carrying capacity from stock wire. It is probably easier to make one gauge of wire and then string pairs than to have custom wire sizes. But I am speculating here.

BTW, I've seen locally (middle GA) the lines in triple triangular bundles. This would prevent both side to side swing and dampen up and down motion of the wires.

Call the 3 phases A, B, and C. Are the phases transmitted in pairs, AB, BC, and AC? Because in the pictures of the power lines I've seen, they are sent in pairs with spacers preventing them from touching. But why pair them at all? Why not just have 3 wires of A, B, and C?

In the picture shown the pairs are (w.r.t. the electrical circuit) to be treated as a single cable. You thus have six cables, two circuits of 3 phase A1,B1,C1 and A2,B2, and C2.

Figure the two circuits have independent load control, one may end up supplying East Metropolis and the other supplying West Metropolis, but possibly with switching available at the transformer station allowing all of Metropolis to be powered by one of the circuits should the other fail. Again I speculate... if you are still curious some intense Google-ing should find you some electrical engineering reference which would explain various configurations which are actually used.

Redundancy makes sense, but I'm not sure about power carrying capacity. If more power is needed, then the turbines in the generator just push harder, and more power goes down through the line. I'm not sure why you need multiple lines for that.

Also if you have twice as many lines don't you get twice the losses?[/QUOTE]
 
  • #8
Thanks, makes sense now.

When I see two conductors with a spacer in between them, I usually think they're at different voltages. But I didn't stop to think what type of insulator could withstand 400 kv, so they're not at different voltages.
 
  • #9
Some intersting info from Wiki-

Bundle conductors

Bundle conductors are used to reduce corona losses and audible noise. Bundle conductors consist of several conductor cables connected by non-conducting spacers. For 220 kV lines, two-conductor bundles are usually used, for 380 kV lines usually three or even four. American Electric Power[4] is building 765 kV lines using six conductors per phase in a bundle. Spacers must resist the forces due to wind, and magnetic forces during a short-circuit.

Bundle conductors are used to increase the amount of current that may be carried in a line. Due to the skin effect, ampacity of conductors is not proportional to cross section, for the larger sizes. Therefore, bundle conductors may carry more current for a given weight.

A bundle conductor results in lower reactance, compared to a single conductor. It reduces corona discharge loss at extra high voltage (EHV) and interference with communication systems. It also reduces voltage gradient in that range of voltage.

As a disadvantage, the bundle conductors have higher wind loading.

From Wikipedia on electrical transmission lines.
 
  • #10
Is it true that only AC transmission lines produce a corona? Or am I wrong? I was thinking most transmission line was DC
 
  • #11
Corona can be made with AC, DC, a single electrostatic discharge, or any combination of these. It is the high voltage ionizing the air (ionized air is a conductor) and then supplying an eddy current into the ionized region that makes the light show.

Electrical transmission lines, however, are AC. DC is impractical due to voltage drops, heat buildup, high cost of DC wiring systems, inability to work through transformers, and a host of other reasons.
 

1. What is the purpose of having 6 pairs of wires in 400KV power lines?

The 6 pairs of wires in 400KV power lines are used to transmit electricity over long distances. The pairs of wires are arranged in a specific way to reduce power loss and maintain the stability of the power grid. Each pair of wires carries a different phase of electricity, which helps to balance the load and improve efficiency.

2. How are the 6 pairs of wires arranged in 400KV power lines?

The 6 pairs of wires are arranged in a specific configuration known as a "bundle". This means that the wires are tightly packed together and arranged in a hexagonal shape. This bundle configuration helps to reduce the amount of space needed for the power lines and also minimizes the effects of electric and magnetic fields on the surrounding environment.

3. What is the significance of 400KV in power lines?

400KV (kilovolts) is a high voltage level used in power lines for long distance transmission. This high voltage helps to reduce power loss during transmission, making the power grid more efficient. It also allows for more power to be transmitted over longer distances without the need for additional power stations.

4. Are there any risks associated with 6 pairs of wires in 400KV power lines?

While 400KV power lines are generally safe, there are some risks associated with them. The high voltage can be dangerous to humans and animals if they come into contact with the wires. There is also a risk of damage to the power lines from extreme weather conditions or other external factors. However, these risks are minimized through proper maintenance and safety protocols.

5. How do 6 pairs of wires in 400KV power lines contribute to the overall functioning of the power grid?

The 6 pairs of wires in 400KV power lines play a crucial role in the overall functioning of the power grid. They help to transmit large amounts of electricity over long distances, maintain the stability of the power grid, and balance the load between different phases of electricity. This allows for reliable and efficient distribution of electricity to homes and businesses.

Similar threads

  • Electrical Engineering
Replies
25
Views
3K
Replies
19
Views
2K
  • Electrical Engineering
Replies
1
Views
771
  • Electrical Engineering
2
Replies
41
Views
14K
Replies
13
Views
918
  • Electrical Engineering
Replies
12
Views
949
Replies
31
Views
4K
  • Electrical Engineering
Replies
33
Views
566
  • Electrical Engineering
Replies
12
Views
1K
  • Electrical Engineering
Replies
10
Views
869
Back
Top