Engineering AC Circuit; find average and reactive power to load (and load V and I)

AI Thread Summary
The circuit analysis involves a load with an impedance of 39 + j26Ω connected to a voltage source of 250V through a line impedance of 1 + j4Ω. The load current (IL) is calculated as 5∠-36.8 A, and the load voltage (VL) is found to be -234∠-3.25 V. To determine the average power delivered to the load, the power factor angle is derived from the difference between the angles of the load current and voltage. The average power is calculated as 975W, indicating the power supplied to the load. Understanding the relationship between voltage, current, and their respective angles is crucial for accurate power calculations.
Color_of_Cyan
Messages
386
Reaction score
0

Homework Statement



In the circuit shown, a load having an impedance of 39 + j26Ω is fed from a voltage source through a line having an impedance of 1 + j4Ω. The rms value of the source voltage is 250V.
a) Calculate the load current IL and voltage VL

b) Calculate the average and reactive power delivered to the load

Homework Equations



V = IR

I = V/R

voltage division

Polar form conversion

j*j = -1

1/j = -javerage power = VIcos∅

cos∅ = power factor

calculating power factorreactive power = (apparent power)sinθ

The Attempt at a Solution



Simplify to this first:



and then voltage division:

VL = (250∠0 deg)*[ (39Ω + 26Ωj)/(40Ω + 30Ωj) ] and in complete polar form:

VL = (250∠0 deg)*[ (46.8∠33.6)/(50∠36.8) ] VL = (234∠-3.25)Vsince the drop VL on the diagram is in the opposite direction thoughVL = (-234∠-3.25)VIL = (250∠0 V) / (50∠36.8 Ω)

IL = 5∠-36.8 ANow, not sure how to get part b from here. Any hints on how to calculate the angle to get power factor? What is meant by the angle between voltage and current to get power factor (and then being able to find average power)?
 
Last edited by a moderator:
Physics news on Phys.org
You have the angle of the load voltage relative to the source voltage, and you have the angle of the load current relative to that same reference, so you should be able to determine the angle of the load current relative to the load voltage.

I think your diagram illustrates the wrong idea, or maybe it is just misleading? The power line is represented by 1 + j4. The load voltage is the voltage across the 39 + j26.

since the drop VL on the diagram is in the opposite direction though
I don't see it.
 
NascentOxygen said:
you should be able to determine the angle of the load current relative to the load voltage.

Sorry for asking, but how exactly do you do this? Any hints? Subtract the angles? It seems confusing.
NascentOxygen said:
The power line is represented by 1 + j4. The load voltage is the voltage across the 39 + j26.

That's right. Were you referring to my simplification though? The simplification was just to find the impedance / voltage across.And I mean there is a + and - for the VL on the question diagram while the battery is the "other way" (isn't it?)
 
Last edited:
Color_of_Cyan said:
Sorry for asking, but how exactly do you do this? Any hints? Subtract the angles? It seems confusing.
If you draw the phasor diagram there should be no confusion. Simply subtract the angles.

And I mean there is a + and - for the VL on the question diagram while the battery is the "other way" (isn't it?)
The + and - are exactly how I'd expect them. No reversal necessary. The + of VL corresponds to the + of the source, so the potential divider equation gives VL as required. (To get current flowing in the load in the direction of the IL arrow, the top of the load must be + with respect to the bottom of the load.)
 
So VL stays positive then.Is the angle you are giving me the same for also determining power factor?And would the angle go: -36.8 - (-3.25) ?
 
Last edited:
Color_of_Cyan said:
Is the angle you are giving me the same for also determining power factor?
Yes, current relative to voltage gives the pf. The question does not ask you for the power factor angle, though. All it asks for is load voltage (relative to source, presumably), and load current (again, presumably relative to souce voltage).

And would the angle go: -36.8 - (-3.25) ?
That looks about right (though it is not asked for).
 
So if

average power = VIcos∅

cos∅ = power factorThen can you calculate the average power as:

Pavg 5*-234(cos(-3.25°)) ?
 
V I cosɸ, but using the power factor angle ɸ that you determined earlier. (As a check, your answer should be the same as if you'd used I².R )
 
That angle was a typo, so

Pavg = 5*-234*cos(-33.55)

Pavg = -975W

=975W supplied?
 