guys some speculation here, followed by a question...
i've been obsessed by the thought the contacts are being eroded by current from the motor
and have tried to operate the braking sequence millisecond by millisecond in my head..
loooking for a relay race between the NO contacts opening and the NC contacts closing
it is necessary for the NO's in upper left to clear before the NC's below close , else we have a near dead short across the supply as shown in post #43
what if... entertain this thought experiment for a moment ... HO12 answered this long ago when he said
when what opens ? The NC's or the NO's ? We established by test that there's no current through the NC's when they open by measuring voltage at junction of the two capacitors if i understood. It drops to zero after motor starts and remains so until braking.
So if the arcing is observed at braking time when the NO's in upper left open, that's not surprising because they are interrupting motor current and it's an induction motor.
Anybody who's arc-welded knows an arc can persist surprisingly long
so in the thought experiment, think millisecond by millisecont from the instant the S relay plunger starts to travel to de-enegrgized position
1. NO contact opens a ten-thousandth of an inch establishing an arc
2. NO contact continues its travel, arc gets longer
3. NC contact makes initial contact , connecting motor to capacitors which are nearly a dead short
4. Current through NC contact consists of current from motor plus any leftovers from the arc - at this instant NC does not yet have full contact pressure so some melting might occur
5. NC contact continues widening its airgap, quenching the arc
6. NC contact establishes full contact pressure and commences to cool whatever metal was melted in 4.
Now here's the speculation
Which comes first ? 4 or 5 ? If NC makes before NO has extinguished its arc, we have a short across supply through a not quite extinguished arc and a not well seated NC contact that's still bouncing... see post #87
Is that scenario plausible?
View attachment 103718
so the relay race i was looking for isn't contact vs contact mechanical travel overlap but contact travel vs arc quenching time overlap.
How does energy deposition between two arcs in series divide?
Is this plausible, guys?
If so, snubber across motor as in post #89 might help NC quench the arc.
That old saying, before you figure out what it is you'll figure out a lot of things it ain't.
If the SSR is SCR based and can't turn off the NO contact until a current zero crossing happens,
then there's an interval where it connects 1000 uf right across the line which could be a bodacious surge.
Looking for holes in that line of thinking
and any thoughts on how to test for it.
old jim