View attachment 103679
During braking, motor's main winding current flows along blue line into new resistor then splits. half going through each capacitor to 115 return.
The half that turns right into CSM2 has a straight shot out other side to 115 return
the half that turns left into CSM1 meanders back through C1-24T then contacts 3-8 of S relay to 115 return.
If i understand the circuit,
Voltage at C1-23N should behave like this
At motor start it will jump up to the 22 VAC/(41DC?) you measured in post #70
(question mark on DC reading is because i think it should be random how much DC you see there, if it's always 41DC i don't understand why
(but that's not unusual ) )
then it will drop to zero as soon as motor reaches speed causing CS to open
when STOP signal de-energizes relay S
allowing its NC contacts to close
voltage will return to C1-23N , and the amount will be whatever the motor makes as an induction generator. That voltage will fade as energy id drained from the motor's inertia.
The resistor should affect rate of energy drain from motor, but how much ? I don't know(the 3 words men fear most).
That resistor HAD to lower the instantaneous current flow into the capacitors, making life easier for your NC contacts.
Since we don't have a 'scope with transient current capture, and my coil didn't tell us anything, we're flying kinda bindIf you can get a reading at C1-23N during a motor braking cycle, we'll divide that by (8 - j 2.65) and figure the amps during braking. (8 is the new resistor you inserted in the circuit...? )
I'm dying of curiosity how much current flows and for how long
That won't tell us the initial current spike but it gives a clue about the motor's behavior, i never did any such experiments and find this interesting
I would suggest
Write this experiment down and put a note inside the machine for the next guy so he'll know what you did
put in a new relay
Surely you know what is average life of these relay contacts?
After say 2/3 of that life, take that relay out and see if we've slowed contact erosion ?
Svein? Tom.G ? Thoughts ?
Kudos to both of you guys , this just might work ! I thought for sure we'd extend coastdown time and de-synchronize the machine.
Keep our fingers crossed this machine runs okay with the extra braking resistor.
HO12 - do you have a contact at AMF ?
Ask him this question, in your own words..
Dear Sir:
We experience short contact life on the AB relays used in model (whichever) Pinsetter and Sweeper
in particular the NC contacts on these relay models
Allen Bradley 700-C220X10
and its replacement
Allen Bradley 700-CF220J
which are used to brake an induction motor by essentially short circuiting it as an induction generator.
We have reason to believe di/dt on contact closure is higher than expected and erodes contact material during contact bounce on make
so we have three questions:
1. What is maximun di'dt for that relay contact on make?
2. What is published subtransient reactance of the motor ? It bears part number (whatever it is)
3. Does motor manufacturer publish, or would you get from his engineering department , estimates of on subtransient fault current available from the motor and initial rate of current rise (di/dt) ?
4. If our suspicion proves correct, transient current erodes the contacts causing premature failure, can you suggest protection for the relay contacts ? This is an industry wide maintenance headache with these machines.
We have equipped one machine with 8 ohms of resistance in series with the braking current path (insert sketch from this post, above).
Coastdown time seems unaffected and we measure (?) amperes of braking current . We will check the relay for contact erosion after ( how many cycles or months ?)
Please advise,
.......
The higher up their organization you send it the better will be the answer you get. I'd find the VP of marketing for AMF bowling products, start at their website and look for "Investor relations - executive team"
If the owner of your company will co-sign with you it'd help.
Lastly, is there an industry magazine you guys read?
In the power plant we loved "Power"magazine because of one regular feature-
a fictional troubleshooter by the name of "Marmaduke Surfaceblow" solved some sticky engineering problem every month
we enjoyed them because they were taken from real events submitted by readers and the writer painted such colorful characters... We young guys all wanted to be confident and blustery and always right like Marmaduke.
http://www.digplanet.com/wiki/Marmaduke_Surfaceblow
If this works you'll want to get the word out to other maintenance men like yourself, submit an article to your trade magazine, editors love real world submissions from the field.
old jim
PS what's voltage at C1-23N when it brakes ? _______