yes I'm learning about fault current contribution from induction motors
We have long known that power engineers have to account for it in short circuit studies, but I'm no expert in those.
and i have taken oscillograms of bus voltage in the power plant during a transfer, those big pump motors (7000 horsepower for boiler feed and 6000 horsepower for reactor coolant) act as generators because the rotor field takes many cycles to decay away.
So
after your little motor has finished arcing the NO contact, which i would think is brief ,
its terminal voltage returns to some number not far from running voltage because the rotor field is still there.
So for the next several line cycles it is an induction generator making probably almost 120 volts.
Next thing that happens is your NC closes connecting the 1000 uf capacitors right across the motor main winding which is still generating ~ 120 volts because the rotor field hasn't collapsed yet.
What happens when you throw a completely discharged 1000 uf capacitor across a generator ? You get a surge of current.
How big a surge ? sixty four dollar question, I've never done that test.
After a lot of reading I'm finding not a real concensus, but the estimates that seem best presented say the surge is 2 to 3 times starting amps, and it's called "Subtransient Fault Current" and it lasts only a fraction of a cycle
starting amps for a 1/3 hp motor ought to be in the range of 5/3 to 7/3 KVA , which at 120 volts is 14 to 19 amps and you reported measuring 22 ..
so perhaps ~60 amps flows through your NC contact at the instant they close
Your resistor will knock down that fault current. I was afraid it'd stretch out motor coastdown but you report it's fine with the resistor.
So we tend to think that'll fix the NC burnup.
But -- that arcing at the NO contact ? How long does it persist ?
If that arc ever fails to go out before the NC contact closes, we then have a path from incoming hot through the arc then through the NC contact to that discharged 1000 uf capacitor. Incoming hot is probably capable of hundreds of amps.
Might that explain your "Gone" NC contacts , unlucky outcome of a relay contact race every now and then ?
Your 8 ohm resistor should limit fault current for that scenario too.
The MOV Varistor will help Mr NO contact extinguish the arc quickly.
and the 8 ohm resistor limits fault current from either source, subtransient from motor or direct from line through arcing NO contact
and diverse methods of protection is good design.
Guess I'm more recapping for my own clarity of thought than anything else
does this help?
Corrections welcome.
Now to figure out how big a varistor we need. ... your "touch test" will be imoprtant.