Figure shows a 50 Hz, high-voltage, transmission line. The relationships between the sending and receiving end voltages and currents are given by the complex ABCD equations:
where 'S' stands for sending-end and 'R' stands for receiving-end
(a) Given the parameter values in TABLE C and an open-circuit received voltage measured as 88.9 kV, calculate the values of
(b) If the line is modeled by the T-circuit of FIGURE 3(b), see if you can estimate the primary line coefficients R, L, G and C. The line is 50 km long.
I am currently doing part (b), if
[ A B ] = [ 1+Z1*Y2 Z1+Z3+Z1*Y2*Z3 ]
[ C D ] = [ Y2 1+Y2*Z3 ]
Then Y2 = C =j0.001349S
Also A=1+Z1*Y2
Z1= (A-1)/Y2
Z1=(0.8698+j0.03542-1) / j0.001349
Z1= 26.268+j96.558 Ω
Z1=Z3
So as Z1 & Z3 in series:
R+jXL = Z1*2
R+jXL = 52.536+j193.116 Ω
R coefficient = R / 50 = 1.051Ω/km
L= XL / 2πf = 193.116 / 2π*50 = 0.614707H
L coefficient = 0.614707 / 50 = 12.294mH/km
G coefficient = 0 as Y2 branch is not resistive only 'imaginary'
XC = 1 / Y2 = -j741.290 which is capacitive
C= 1/ XC*2πf = 1 / j741.290*2π*50 = 4.29μF
C coefficient = 4.29μF / 50 = 85.88pF/km
How does that look to you smarter people?