russ_watters
Mentor
- 23,694
- 11,133
You're misunderstanding what is going on. If you tried to combine the two signals on one wire, they'd cancel, but the two signals aren't traveling down the same wire, they are traveling down separate wires. Just draw yourself a graph!zgozvrm said:And, to re-iterate, if the 2 "halves" were 180 degrees out of phase with each other, they would not combine to form 240 volts; they would cancel each other out to 0 volts (assuming of course that the average value of the sine wave is 0 volts).
This is correct...and it is why when you feed both wires into the same device, you are now using each as the reference for the other.zgozvrm said:A single phase voltage, by itself, has no "direction" and therefore no phase angle. So, the generators can both supply 230 volts (that is, they each have a potential difference of 230 volts between their individual terminals), but each voltage waveform has no angle. Not until there is some physical connection between the 2 voltages, can you have a phase difference (phase angle) between them.
When you measure the voltage between the two wires, you get 240V because when one is +120V, the other is -120V.